NOC Card - Modbus TCP Polling Unstable Data

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • NOC Card - Modbus TCP Polling Unstable Data
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
10
ciupol
Lieutenant ciupol
9
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
RuchirSomani
Crewman RuchirSomani
Crewman

Posted: ‎2025-07-14 09:46 AM

0 Likes
4
87
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-14 09:46 AM

NOC Card - Modbus TCP Polling Unstable Data

We are facing below challenge while using NOC card 0301.2

 

    1. Using READ_VAR block, not at single Modbus TCP request is getting generated.

       

    2. When we used default Modbus TCP feature for NOC card, till the 1st request all the activity runs smoothly. As soon as we generate 2nd request, all the MFM data in M580 goes haywire. Please find attached videos for reference.

Please suggest proper solution for this problem as we have to use 14 Nos. of request with each request having data polling of approx. 120 Nos. of 16 bit registers.

Attachments
Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2025-07-15 12:51 AM

0 Likes
1
85
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 12:51 AM

How are you triggering the read activity as it seems every second read is OK, but you are zeroing the data in between. 

What are you reading from?  is it a serial gateway?

 


Have you raised the issue with your technical support team?

Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
RuchirSomani
Crewman RuchirSomani
Crewman

Posted: ‎2025-07-15 10:04 AM

In response to Trinxs1
0 Likes
0
65
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 10:04 AM

Hi,

 

1. Yes we are reading all the request every 1 second.

2. We have selected option of ZEROING the last value - considering it shall set the parameters value to ZERO if any device goes offline or query goes unresponsive.
Is it because of this setting that the values are intermittently going to ZERO ??

3. We are reading the value for Modbus Serial to TCP Gateway device.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
YONGHO-KIM
Lieutenant JG YONGHO-KIM Lieutenant JG
Lieutenant JG

Posted: ‎2025-07-15 09:40 PM

2 Likes
0
67
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 09:40 PM

1. Please try reading Modbus TCP data using the READ_VAR block.

  1. Refer to the attached example below.
  2. If you have any questions regarding the configuration, feel free to ask.
  3. The example configuration is as follows:
  • Target IP: 172.168.12.101
  • Target Address: 1
  • Reads 96 registers starting from address 3000, and 32 registers starting from address 3096, using Holding Registers.
  •   YONGHOKIM_0-1752640746986.pngYONGHOKIM_1-1752640792183.png

     

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2025-07-17 12:32 AM

1 Like
0
29
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-17 12:32 AM

Hello Ruchir,

 

As you are reading from a Modbus device using a gateway in between you must make sure that your gateway is able to handle multiple (2 in your case now) Modbus TCP messages at the same time.

Also the IO-scanning functionality uses a relative fast retry mechanism. Specially when the gateway modbus device doesn't respond fast enough (it's baudrate is limited, not 100MB), it will cause retry's to be sent out before the gateway was even ready to respond,specially having more than 1 message to be sent/answered. You can try using the Gateway/Bridge device checkbox, but this is only available when you define the NOC card as type BMENOC301.4 (instead of .2). 

RoozeeR_0-1752737357128.png

Note the 301.4 is the same hardware as 301.2, only check the firmware which must be >=2.11.

If that doesn't solve your issue use READ_VAR function blocks.

R.Roozee
Sr Solution Architect (SAE Master)
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of