Dear Sir
Could someone advise the PLC TSXP573623am has performed to operated or not.
We can't connected to it. the LED has blink in "ERR" and "I/O" As diagostic table, The fualt is "FAULT on BUS X"
Maitree R.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-17 09:54 PM
The first step is to ensure if you have a backplane with expansion ports the backplane is terminated correctly with the TSXTLYEX A / B terminators.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-18 01:53 AM
Thank you, we has missed to install TSXTLYEX part.