Posted: 2021-03-23 02:37 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 02:37 AM
Hello everyone,
I am new to Schneider and EcoStruxure. I am now programming a Modicon M221 with the EcoStruxure Basic Software. It's a simple application that requires a timer, and I want to be able to change the PRESET value through an HMI. I was only able to find a TIMER block that allows an input to start the timer, a fixed PRESET value, and an output Q.
Is it possible to make the PRESET a variable and change that variable through the HMI?
Thank you in advance for your time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-24 11:22 PM
Hello,
You can reach your goal on the follow way.
You can write a variabel (as example %MW0 which is reachable via Modbus) in the instance of the Timer.
If you use %TM*.P you can overwrite the preseted Time value. (* = number of timer)
best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.