Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Search in
Posted: 2021-03-23 10:50 PM . Last Modified: 2021-03-23 10:51 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-23 10:50 PM . Last Modified: 2021-03-23 10:51 PM
Native "Health Timeout" and "Last Value" settings in Concept/Unity/Control Expert IO Scanner allows inter-PLC communication with fallback to "0" in event of comms loss (built-in-watchdog)
I've now transitioned to Global Data (Multicast Publisher/Subscriber inter-PLC comms). Do I need to build my own watchdog bit into the Global Data DDTs or is there a similar "fallback to 0" feature?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-28 04:45 PM
I would strongly recommend installing a watchdog as the first or last register in the data transfer from each PLC. I would also ensure that each participating PLC publishes at least a watchdog.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.