Posted: 2021-03-16 09:36 AM
Dear Supporter,
After using unity pro from v4 to v13 - I'm facing more challenges day by days with higher versions.
My application is working fine (running plant) except I couldn't able to upload. I mean, in the middle of upload its stopping and popping up error - Transfer project from PLC failed and the upload process terminates.
FYKI - I'm lucky that I'm having original backup. The PLC backup's is with UPLOAD INFO OK.
Let me explain step by step about my activity and errors caused.
STEP 1 - Just entered syslog IP address and port number in project settings. Done rebuild all and it was successful.
STEP 2 - Downloaded the PLC program in M580 redundant systems.
STEP 3 - Then after this, Normally I came offline and just made a "REBUILD ALL", the process is starting and getting hanged at 64% generating variables.
STEP 4 - After waiting for 15 min also, the 64% is hanging up in the same spot. Its not accepting "STOP" command to stop the rebuild process. I have only option to close the software from the task manager.
STEP 5 - For parallel checking - I used other laptop with same backup. Still the issues is similar.
Attached here with the images for deeper understanding.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-28 01:04 AM
Dear Brother,
Issue was solved when upgrading V13 backup to V13.1.
It seems to a problem in V13 setup file. So I installed V13.1 and automatically all issues were fixed.
Thanks for your support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-18 03:48 PM
A few standard checks and I know this may seem tedious.
When upgrading from V4 did you export and re import the project into V13 or did you use the archive (.STA) file? I sometimes find with such a large jump in versions it is best to update the libraries as well as the catalogue.
How much memory does the CPU have spare?
Have you update V13 with all of the latest hot fixes?
If there is still an issue I would raise this with your local technical support team. I am not tech support, but I have not seen this issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-28 01:04 AM
Dear Brother,
Issue was solved when upgrading V13 backup to V13.1.
It seems to a problem in V13 setup file. So I installed V13.1 and automatically all issues were fixed.
Thanks for your support.