Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

M580 safety unrecoverable error when minor online edits (error codes %SW124 = 0xEC10)

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Re: M580 safety unrecoverable error when minor online edits (error codes %SW124 = 0xEC10)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
ciupol
Lieutenant ciupol
9
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Solved
erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-03-02 12:41 AM

0 Likes
20
3475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-02 12:41 AM

M580 safety unrecoverable error when minor online edits (error codes %SW124 = 0xEC10)

Hello, 

 

I have a program in Control Expert v16, in which when I do a minor online update (e.g. change the tag of the function block input) the PLC goes into unrecoverable error and crashes. 

 

I attach below a video with the example. 

 

The message displayed in CE is:
CSA has downloaded to PLC. Execution has failed.On-line modification error.

 

Monitoring the %SW124 online I have seen:

%SW124 = 0xEC10

 

and also 0xEC04.

 

Please let me know if you can help, 

 

Thanks, 

Attachments
Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-07-28 10:40 PM

0 Likes
0
3034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-28 10:40 PM

My solution was to revert back to ECE v15.1!

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 20
gchorta
gchorta Support
Support

Posted: ‎2024-03-05 06:04 AM

1 Like
2
3442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-05 06:04 AM

Hello @erik.cornelsen ,

I would suggest you to raise a case with your local country support for a proper investigation as it is related to a crash and apparently you can replicate it all the time.

When you open a case make sure to include your video and:

- CPU model
- CPU Firmware
- Diagnostic Files
- Application backup

Best Regards,

Gabriel Horta

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-03-06 12:22 AM

In response to gchorta
0 Likes
1
3416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-06 12:22 AM

Bom dia @gchorta, obrigado pelo suporte.  

 

I already opened a case with the local support and send all the information you mentioned. 
Unfortunately the problem still not solved and it will impact my team a lot during commissioning, because online edits it is a key function expected from the M580 Safe PAC. 

 

Please let me know if you can help, 

Kind regards, 

Erik Cornelsen

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

bruno.bodet
Crewman bruno.bodet
Crewman

Posted: ‎2024-07-26 03:30 AM

In response to erik.cornelsen
0 Likes
0
3084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-26 03:30 AM

Hello,

We quickly discovered this problem when we installed ControlExpert V16.

The problem was passed on to local support, who took charge of the international “level 3”.

Have you had any feedback since opening your post?

Thank you

Bruno

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-07-28 01:24 PM

0 Likes
1
3058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-28 01:24 PM

Some of my co workers using ECE 16.0 with M580 Safety have also reported this problem.  We too are waiting on a solution from tech support.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

bruno.bodet
Crewman bruno.bodet
Crewman

Posted: ‎2024-07-28 09:59 PM

In response to MatthewM
0 Likes
0
3022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-28 09:59 PM

Hello,
Thank you for your reply.
The problem has also gone up, so we'll have to go back to V15 in the meantime.
Best regards

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-07-28 10:40 PM

0 Likes
0
3035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-28 10:40 PM

My solution was to revert back to ECE v15.1!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-07-29 08:45 PM

0 Likes
4
2995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-29 08:45 PM

We can't go back to v15.3 due to serious defects in a number of the built in safety functions (S_MUTING_PAR for one).  We were forced to go to v16 where they have been fixed, only to find stability issues.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2024-07-30 09:15 PM

In response to MatthewM
0 Likes
1
2964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-30 09:15 PM

Please note that for safety only V15.1 SP1 is TUV certified.  We are expecting a release within the next few weeks of the next release of CE which is TUV certified.  This will also have a new firmware for the CPU to install.

 

Trinxs
Senior Technical Sales Consultant - PAC
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2024-07-30 09:18 PM

0 Likes
1
2963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-30 09:18 PM

It may not help but is also a worth a try.  If there is a corruption in the project sometimes it is worth exporting the project, closing the application and then importing the exported version and rebuilding it.
out of curiosity is CE running on WIN 11 or WIN 10?

Trinxs
Senior Technical Sales Consultant - PAC
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-07-31 12:02 AM

In response to Trinxs1
0 Likes
0
2934
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-31 12:02 AM

In my case it was WIN 10 and it was not corruption in the project, because it also does with a brand new fresh project.  
Is CE v15.3 TUV certified and what's the plan for the TUV certification of the v16? 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-07-31 12:06 AM

In response to MatthewM
0 Likes
1
2933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-31 12:06 AM

It worth check if the CE v16 is TUV certified for the safety, it was still not when I first used it earlier this year. 

Which other safety functions that you tested had issues?
Thanks  

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-07-31 12:53 PM

In response to Trinxs1
0 Likes
0
2900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-31 12:53 PM

Hi @Trinxs1, TUV certification or not, it is impossible for us to use anything earlier than v16 due to the serious defects we discovered in the S_MUTING_PAR function which we need to use.  v16 also fixes three other safety functions that had problems which I had not discovered yet.  I found it quite alarming.  We had to make the call that we would have to commission with v16 on the promise that the TUV certification was coming soon.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-07-31 01:02 PM

In response to erik.cornelsen
0 Likes
0
2900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-31 01:02 PM

The only one I uncovered myself was S_MUTING_PAR where I found a basic sequencing issue and a major deadlock issue.  Here are other safety function fixes in the release notes for v16 that are significant:

PEP0499448R  UP13.1 bug in FB S_MUTING_PAR  PLCCE-8

PEP0619623R  CE14.1 safety DFB S_EQUIVALENT fails on dead lock  PLCCE-151

PEP0664455R  CE V15.0 - the status word of S_EDM doesn't switch properly  PLCCE-3252

PEP1060720R  DFB - S_OUTCONTROL can go into deadlock state  PLCCE-4920

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-07-31 01:33 PM . Last Modified: ‎2024-07-31 01:37 PM

0 Likes
1
2886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-31 01:33 PM . Last Modified: ‎2024-07-31 01:37 PM

Tech support have shared ControlExpert_V160_HF001 which contains ControlExpert_V160_HF007, which hopefully addresses the crashing issue:

 

ControlExpert_V160_HF007 has been developed to address a specific issue concerning
“M580 CPU cessation of operation, EC10 and three red LEDs reported” in case actions
taken by this sequence:
a) On an application previously Rebuild All connected to a M580 CPU.
b) Create/open a section code and add several EFBs
c) Do a Build Changes
d) Remove one of them (not all) inside this section code, and remove also instance
inside Data Editor.
e) Do a Build Changes

 

A colleague found it is also downloadable from the SE website.  They found it here:

https://www.se.com/myschneider/catalogBrowse/nz/en/range/548#software-and-firmware

and search on:

ControlExpert_V160_HF001

 

I think you have to ignore the comments in the release notes about TUV for v16, which it does not have yet!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

bruno.bodet
Crewman bruno.bodet
Crewman

Posted: ‎2024-07-31 10:30 PM

In response to MatthewM
1 Like
0
2849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-31 10:30 PM

Hello,


I can confirm that the patch is now operational and solves the problem of the M5280S crashing when using personal DFB blocks.
Thanks to the SE team for their responsiveness
Bruno

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

vroman_cedric
vroman_cedric
Cadet

Posted: ‎2024-09-25 06:51 AM

0 Likes
3
2489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-25 06:51 AM

Bonjour

 

J'ai aussi un problème de plantage cpu M580 6040S même avec le HotFix installé.

 

J'attend un retour de Schneider

Cedric

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-09-29 11:58 PM

In response to vroman_cedric
0 Likes
2
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-29 11:58 PM

Bonjour Cedric, 

 

Dans quelles conditions le plantage CPU se reproduit ?

Quels sont vos versions firmware et Control Expert ?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

vroman_cedric
vroman_cedric
Cadet

Posted: ‎2024-09-30 12:28 PM

In response to erik.cornelsen
0 Likes
1
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-30 12:28 PM

Bonjour

 

Control Expert V16.0 Hotfix 1

CPU 6040S v3.30

la cpu plante après plusiers modification successive dans la tache non safety, quelque soit la modification.

 

Juste le message suivant :

 

"Le CSA a été chargé dans l'automate, l'exécution a échoué"

 

 

 

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

erik.cornelsen
Ensign erik.cornelsen
Ensign

Posted: ‎2024-10-01 10:09 AM

In response to vroman_cedric
0 Likes
0
2368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-01 10:09 AM

Avez-vous essayez avec le dernier firmware ?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2024-10-01 09:42 PM

0 Likes
0
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-01 09:42 PM

Please note that V16.0 HF001 is certified by TUV for use in safety systems.  If you wish to view the certificate please refer to the link FS-PRODUCTS (tuvasi.com).

Trinxs
Senior Technical Sales Consultant - PAC
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of