Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84751members
354180posts

M580 monitoring

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Solved
israa
Crewman Crewman
Crewman
0 Likes
1
1310

M580 monitoring

Hello all,

 

In one of our Project client requested to include PLC( M580 Hot standby) internal battery low alarm status which is to be configured in PLC/SCADA.

 

is there maybe a system bit to monitor the battery state of the M580, knowing that M580 has no internal battery..

 

Is it possible or not ?

 

Isra 

Tags (1)

Accepted Solutions
Robert_Willis
Ensign Ensign
Ensign

Re: M580 monitoring

1. The M580 does not rely on a battery for memory backup so there is nothing to monitor.

 

2. They can monitor the status of the M580 CPU and HSBY functionality via the Device DDT.

 

3. The Redundant Power Supplies when mounted in a BMEXBP0602 or BMEXBP1002 rack can provide diagnostic from each power supply. NOTE: This only applies to the primary rack 

 

4. The status of all I/O can be monitored vis the associated Device DDT.

 

5. I would use the Schneider Electric OPC-DA or OPC-US server to directly read the unlocated variables in the Modicon Quantum controller.

See Answer In Context

Tags (1)
1 Reply 1
Robert_Willis
Ensign Ensign
Ensign

Re: M580 monitoring

1. The M580 does not rely on a battery for memory backup so there is nothing to monitor.

 

2. They can monitor the status of the M580 CPU and HSBY functionality via the Device DDT.

 

3. The Redundant Power Supplies when mounted in a BMEXBP0602 or BMEXBP1002 rack can provide diagnostic from each power supply. NOTE: This only applies to the primary rack 

 

4. The status of all I/O can be monitored vis the associated Device DDT.

 

5. I would use the Schneider Electric OPC-DA or OPC-US server to directly read the unlocated variables in the Modicon Quantum controller.