M580 communication with HMIGXU5512 is working only in CPU service port, why ?

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M580 communication with HMIGXU5512 is working only in CPU service port, why ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Control Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Solved
ArunrajPremraj
Ensign ArunrajPremraj Ensign
Ensign

Posted: ‎2022-03-11 02:02 AM

0 Likes
2
2523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-11 02:02 AM

M580 communication with HMIGXU5512 is working only in CPU service port, why ?

Hi,

 

I am trying to establish a communication with HMI using ETH- 1 and ETH-2 ports or the M580 CPU ,  But HMI is not gives " plc communication failed " error. 

 

But when i connect it to CPU service port it works,  I tried port mirroring also. .still not working. 

 

i dont want to use Service port for communication purpose. 

 

i have a switch connected to ETH-1 port and the HMI and other devices are communicating via the switch. 

 

HMI communication works only if i connect to CPU Service port. 

 

I have checked the ETH-1 and ETH-2 ports. both are healthy and can upload and download , ping IP's and are healthy. .. 

 

what is the issue here..?   

 

 

thanks.

Labels
  • Labels:
  • 01. Modicon M340 PAC
  • 02. Modicon M580 ePAC
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DenisGoyette
Crewman DenisGoyette Crewman
Crewman

Posted: ‎2022-03-11 05:48 AM

0 Likes
1
2505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-11 05:48 AM

Hi,

 

What model of M580 CPU is this? If it's a xx40 model, ie. BMEP582040, I remember seeing that the 2 bottom ports are used (reserved) for the ERIO architecture. Other type of traffic will not get through (unless using specific cards or connexium switches). You would have the same behavior if you would try to do modbus TCP/IP IO scanning out of those 2 ports.

 

You do not get that behavior out of the xx20 models, since they do not support ERIO.

 

So you'll need to use the service port of the cpu to connect your HMI, or add a BMENOC card to your setup.

 

I can't find the documentation explaining that at the moment unfortunately.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
DenisGoyette
Crewman DenisGoyette Crewman
Crewman

Posted: ‎2022-03-11 05:48 AM

0 Likes
1
2506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-11 05:48 AM

Hi,

 

What model of M580 CPU is this? If it's a xx40 model, ie. BMEP582040, I remember seeing that the 2 bottom ports are used (reserved) for the ERIO architecture. Other type of traffic will not get through (unless using specific cards or connexium switches). You would have the same behavior if you would try to do modbus TCP/IP IO scanning out of those 2 ports.

 

You do not get that behavior out of the xx20 models, since they do not support ERIO.

 

So you'll need to use the service port of the cpu to connect your HMI, or add a BMENOC card to your setup.

 

I can't find the documentation explaining that at the moment unfortunately.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ArunrajPremraj
Ensign ArunrajPremraj Ensign
Ensign

Posted: ‎2022-03-13 09:31 PM

In response to DenisGoyette
0 Likes
0
2443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-13 09:31 PM

Thank you very much for the reply,  I am using BMEP582040 exactly.  I will try to use a connexium switch and see if it works.  I possible can u guide me or direct me on how to configure Connexium Switch ports to connect to HMI?

 

Thanks in advance!!!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of