Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
Back to Modicon PAC Forum
ArunrajPremraj
ArunrajPremraj Contributor
Contributor
Posted: ‎2022-03-15 04:52 AM
2
3684
Dear All,
My customer has asked some questions related to M580 safety PLC communication blocks for which i need answers. the questions are as below,
1) What is the Maximum no. of Parallel/simultaneous TCP/IP connections that SIL CPU supports as modbus client?
2) What is the Maximum no. of Outstanding modbus requests?
3 )What is Maximum Buffer size for keeping Pending modbus requests?
I would really appreciate if someone can answer any of this
  • Communication Limitation
  • m580
  • modbus
  • SIL
DanielWeber
DanielWeber Contributor
Contributor
Posted: ‎2022-03-16 04:02 AM
1
3656
there is no specificity with Safety - SIL Modbus communication limitations. Limitations are for Modbus TCP/IP.
You should find all the answers in the M580 Hardware Reference Manual, page 28/29
Modicon M580, Hardware Reference Manual
I hope it helps.
DanielWeber
Contributor
1
3657
I hope it helps.
BevanWeiss
BevanWeiss
Champion
Posted: ‎2022-03-16 02:42 PM
In response to DanielWeber
If you are talking about safe communications then you should reference the Safety Manual
https://www.se.com/au/en/download/document/QGH46982/
In this you would use
S_WR_ETH_MX / S_WR_ETH_MX2
S_RD_ETH_MX / S_RD_ETH_MX2
Which require unique ID fields for all safe communication on the network (where there could be the possibility of unintended cross-over of base communication 'channels').
This essentially means if you have 100 PLCs, each communicating to 3 PLCs, then you would have 100 x 3 x 2 (bidirectional) channels.. = 600.
The ID is an integer, so you're unlikely to run into practical limitations with this before you would start to hit network limitations.
Co-ordinating the ID fields to ensure no duplicates is generally a little trickier however.  So you'd want to allow for ranges for each PLC.  Perhaps allowing 10 or so 'slots', 5 in each direction.  So PLC1 would get IDs 10-19, PLC2 IDs 20-29.. etc etc.