My customer has asked some questions related to M580 safety PLC communication blocks for which i need answers. the questions are as below,
1) What is the Maximum no. of Parallel/simultaneous TCP/IP connections that SIL CPU supports as modbus client?
2) What is the Maximum no. of Outstanding modbus requests?
3 )What is Maximum Buffer size for keeping Pending modbus requests?
I would really appreciate if someone can answer any of this
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-16 04:02 AM
Hello,
there is no specificity with Safety - SIL Modbus communication limitations. Limitations are for Modbus TCP/IP.
You should find all the answers in the M580 Hardware Reference Manual, page 28/29
Modicon M580, Hardware Reference Manual
I hope it helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-16 04:02 AM
Hello,
there is no specificity with Safety - SIL Modbus communication limitations. Limitations are for Modbus TCP/IP.
You should find all the answers in the M580 Hardware Reference Manual, page 28/29
Modicon M580, Hardware Reference Manual
I hope it helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-16 02:42 PM
If you are talking about safe communications then you should reference the Safety Manual
https://www.se.com/au/en/download/document/QGH46982/
In this you would use
S_WR_ETH_MX / S_WR_ETH_MX2
S_RD_ETH_MX / S_RD_ETH_MX2
Which require unique ID fields for all safe communication on the network (where there could be the possibility of unintended cross-over of base communication 'channels').
This essentially means if you have 100 PLCs, each communicating to 3 PLCs, then you would have 100 x 3 x 2 (bidirectional) channels.. = 600.
The ID is an integer, so you're unlikely to run into practical limitations with this before you would start to hit network limitations.
Co-ordinating the ID fields to ensure no duplicates is generally a little trickier however. So you'd want to allow for ranges for each PLC. Perhaps allowing 10 or so 'slots', 5 in each direction. So PLC1 would get IDs 10-19, PLC2 IDs 20-29.. etc etc.