Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

M580 Safety use of Analog Inputs (BMXSAI0410)

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M580 Safety use of Analog Inputs (BMXSAI0410)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
MatthewM
MatthewM
Mentor

Posted: ‎2024-06-11 02:34 PM

0 Likes
4
3103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-11 02:34 PM

M580 Safety use of Analog Inputs (BMXSAI0410)

Hi everyone,

 

Has anyone out there used analogue inputs in safety applications?  We have a BMXSAI0410.  There are no functions available in safety code for scaling from raw to EU.  Do we just get used to the idea of working in raw only, or do we scale it manually with half a dozen math blocks?

 

Thanks

Labels
  • Labels:
  • 03. Modicon PAC Safety
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Farzad_Samimi
Farzad_Samimi Contributor
Contributor

Posted: ‎2024-06-13 05:18 AM

0 Likes
1
3030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 05:18 AM

Hi Matthew,

There is a demo project for M580s when you install Control Expert, there is a DFB create for safety section that scales the analog input.

 

 

 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Hennie_Smith
Hennie_Smith Mentor
Mentor

Posted: ‎2024-06-11 09:37 PM

0 Likes
1
3068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-11 09:37 PM

Hi. The SAFE sections should be used only for the safety logic based on the Cause&Effect matrix compiled during the Risk assessment. (Comparisons will need to be with the RAW values). To scale the values for HMI/SCADA purposes you can read the values via the interface in the PROCESS sections and scale it accordingly.

sesa60976_bridg_0-1718166682687.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
MatthewM
Mentor

Posted: ‎2024-06-12 08:45 PM

In response to Hennie_Smith
0 Likes
0
3048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 08:45 PM

Thanks for the reply.  Yes I am already scaling in the Process section for SCADA, but I do find it odd that it is expected to use RAW in the safety application.  I thought the days of having to use RAW died with 984.  Apparently not.

Cheers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Farzad_Samimi
Farzad_Samimi Contributor
Contributor

Posted: ‎2024-06-13 05:18 AM

0 Likes
1
3031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-13 05:18 AM

Hi Matthew,

There is a demo project for M580s when you install Control Expert, there is a DFB create for safety section that scales the analog input.

 

 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
MatthewM
Mentor

Posted: ‎2024-06-16 04:12 PM . Last Modified: ‎2024-06-16 04:14 PM

In response to Farzad_Samimi
0 Likes
0
2986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-16 04:12 PM . Last Modified: ‎2024-06-16 04:14 PM

Thanks for that.  I had not found that demo app.  I will mark this as a solution, even though I requires making a DFB (using system Safety Functions).  The client site does not want is to create DFBs for safety, so I will either have to replicate the contents of the DFB for each analog (only 2), or just live with using RAW.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore