I have configured my Ethernet Network connectio (called Ethernet_1) and have linked it to Ethernet Channel 3 on the M340 PLC. I've set it to use ETH TCP IP.
When I Set the Address in Control Expert I select MODBUS TCP and then go to communication parameters / driver settings. From there I can select Modbus test, enter the IP address of the PLC and it connects. When I click start I get lots of activity on my network switch.
The problem is when I try to go online from Control Expert using the MODBUS TCP:SYS connection. I get the following:
Any ideas on what I'm doing wrong?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-17 08:25 PM
the :SYS setting is used for USB, when using TCPIP you need to set the Address to the actual address
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-18 06:59 AM
So, you have probably figured out that I'm a newbie to Schneider PLC's. Thank you for your gracious response.