Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84468members
353683posts

M580 PIDFF

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

gcummings
Cadet
0 Likes
2
840

M580 PIDFF

PIDFF Block FF Input, I am using FF with WW, My ff_int & otff_int = 0, my ff_sup & otff_sup = 40, I would expect when FF input = a number >= 40 the output should increase by that amount. That is not what I am seeing. Can anyone tell me what I am missing her? The loop is in Auto mode.

 

Anyone have any idea what I am missing here?

 

.outff = FF input

Tags (1)
2 Replies 2
john_m
Ensign
Ensign
0 Likes
0
828

Re: M580 PIDFF

Hi

I don't know the solution for your pid but used a Feedforward is always complicated when  you have dispersion on your process. An open loop is not reassuring. The best alternative is to use Relaxc ( available under EAE and unity [trail version available on exchange))

See this video https://www.youtube.com/watch?v=wePez3n0h-E

 

Furthermore  Relaxc can replace predictive control, IMC, LQG, LQR, Kalman, ...  and of course the PID.

 

Stay tuned

 

Tags (2)
AlastairF
Lieutenant Lieutenant
Lieutenant
0 Likes
0
812

Re: M580 PIDFF

Have you looked at the description of the PIDFF block in the Help file? See the Parametering section.

I think your problem is that you have ff_sup = ff_inf (you mention value of 40 for both).

If these are equal the FeedForward component is ignored ie not added to the output.

 

There is no need to go and buy a commercial add-on to get capable process control for most applications.