M580 Modbus communication Woes

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M580 Modbus communication Woes
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
11
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
9
ciupol
Lt. Commander ciupol
9
RoozeeR
Lt. Commander RoozeeR Lt. Commander
8
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
Terry_Howsham
Terry_Howsham
Cadet

Posted: ‎2024-10-30 01:21 PM

0 Likes
3
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-30 01:21 PM

M580 Modbus communication Woes

I have a project up with a Schnieder M580 PLC and with a BMENOC0301 card.
The majority of the comms will be Modbus TCP/IP.

I need to check Modbus TCP/IP comms as I am setting up a C-More CM5 to talk to it.

Does Control Expert any unique setup for Enabling Modbus TCP/IP?

I have tried to just show a few values to no success. (%MW4001, %MW4002, etc.)

I cannot see any values remotely via Modscan64.

My IP Address is 192.168.6.3

Modscan64 sees this as a valid IP address.

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
Lieutenant

Posted: ‎2024-11-04 08:39 PM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-04 08:39 PM

Please check if the information below is correct

1) M580 PLC (BMENOC0301) = Modbus Slave, Modscan64 = Modbus Master
2) Is the ping test from PC running Modscan64 to BMENOC0301 normal?
3) If Modscan64 is Modbus Master, %MW4001 and %MW4002 data must be set as follows to read from PLC.

1.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Bosswaffle
Lt. Commander Bosswaffle
Lt. Commander

Posted: ‎2024-11-06 10:17 AM

0 Likes
0
1136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-06 10:17 AM

Does Control Expert any unique setup for Enabling Modbus TCP/IP?

If you have the default security configuration for your NOC0301 then yes, the "Access Control" portion will stop communications from working. Try disabling that list or adding your computer's IP.

Reply

Link copied. Please paste this link to share this article on your social media post.

gcummings
Ensign gcummings
Ensign

Posted: ‎2024-11-06 10:16 PM

0 Likes
0
1117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-06 10:16 PM

If you are trying to reach the first Analog Output. Try just %MW0001 and %MW0002, C-more might be offset by 1. I use AVEVA Edge 2023 with the Schne driver. It is exact, no offset. C-more is a very cheap and dirty (Notice, I didn't say robust) HMI. I would not recommend it. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore