Hello,
Simple question that I cannot find the answer to.
If I have one generic modbus device configured (either via CPU or BMENOC0301) and need to read ~700 registers, I would then create 6 different "Requests" as the maximum registers per request is 125.
But how many concurrent connections would this open to the Modbus server, will there be 1 or 6 simultaneous connections to the server?
If someone have an link to somewere where exactly this is explained I would be greatful.
Also how the request and connection handling of the io scanner in general is of interest
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-29 09:02 AM
Here is the answer if someone else is wondering the same as I did.
According to what I can see, each configured request will open its own TCP connection towards the modbus server.
From the wireshark logg you can see that as soon as the modbus server is started, the M580 establishes 2 separate TCP connection [SYN, ACK] with source ports 3456 and 4737 against the modbus server on 502.
Same source ports are being used (same TCP connections kept open) until the server is stopped [FIN, ACK].
Attached are 3 pictures:
1st: Request configuration
2nd: Wireshark screenshot from when Modbus server is started
3rd: Wireshark screenshot from when Modbus server is stopped
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-23 09:18 PM
1) I don't know what model the device is communicating with or what specifications it has from the slave's point of view, IP and port number are requests from the same master, so it is expected to be able to handle them.
2) If BMENOC0301 is also operated as a server, it can handle up to 64 units.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-24 03:27 AM
Hi, and thanks for the reply
We are communicating to all kinds of devices, just depending on what different customers are using.
But usually you can find in their manuals that the Modbus server can handle eg. 8 simultaneous client connections via port 502.
So the main question is how many TCP connections the M580 will have open simultaneously towards any random (non Schneider) slave, when I have configured 1 "Generic Modbus Devices" which has 6 "Requests" configured.
What makes me wonder is when each request have their own "Connection bit", which could indicate they are each having their own TCP connection open towards the slave.
So I assume the answer is either 1, if the requests are being handled one at a time, or 6 if the requests are being polled all at the same time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-24 11:04 PM
Based on the configuration you've described, if you have configured 1 "Generic Modbus Device" with 6 "Requests" and each request has its own "Connection bit," it indicates that each request can have its own TCP connection open towards the slave. Therefore, in this scenario, the M580 could have 6 TCP connections open simultaneously towards the non-Schneider slave, assuming that each request can be handled independently.
This means that if the requests are being polled simultaneously, the M580 could have 6 open TCP connections at the same time. I hope this clarifies the situation for you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-25 05:09 AM
Thank you for your effort in replying. I do really appreciate it
But you answer implify that you are not sure about the actual situation, and it then only becomse a reformulation of my original question.
What I would need to know is if the polls are actually being performed simultaneously or one at a time.
A better way to ask the same thing is maybe: will the polls have different source ports?
I do not have any CPU available for the moment, but I guess I will have to check it with wireshark as soon as I get my hands on the hardware.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-28 05:40 PM
I share the test result value using Modbus Simulator.
1. Test conditions
1) Poll Delay 1s
2) Poll Delay 0.1s
2. Poll Delay 1s
- Interval of the register requesting 125 pieces approximately 2 ms
3. Poll Delay 0.1s
- Interval of the register requesting 125 pieces approximately 2 ms
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-29 09:02 AM
Here is the answer if someone else is wondering the same as I did.
According to what I can see, each configured request will open its own TCP connection towards the modbus server.
From the wireshark logg you can see that as soon as the modbus server is started, the M580 establishes 2 separate TCP connection [SYN, ACK] with source ports 3456 and 4737 against the modbus server on 502.
Same source ports are being used (same TCP connections kept open) until the server is stopped [FIN, ACK].
Attached are 3 pictures:
1st: Request configuration
2nd: Wireshark screenshot from when Modbus server is started
3rd: Wireshark screenshot from when Modbus server is stopped
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-04 09:09 PM
1st: Request configuration
> If it is possible to share PLC project file, I will review it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-05 08:26 PM . Last Modified: 2024-11-05 08:30 PM
Schnabber and Yongho-Kim the answer is that for the DTM instance created for one device with multiple requests there will be one connection for each request even though the same IP address is targeted. This has been confirmed as you have done by Wireshark and by the collective intelligence in the global technical presales team.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-06 08:22 PM
Just for fun, can you get onto the webpage for the CPU or BMENOC0301, whichever is being used, and look at the connection list there? It may list the same IP twice, indicating the two connections. I am sure I have seen it before somewhere.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-07 09:34 PM
I can do so when i get my hands on an CPU again, might be next week. Would be good if the webpage indicated not only active connections but all connections that's configured (trying to connect).