M340 read MODBUS device value
Hi all,
I'm new to Schneider PLC. I had try some READ VAR tutorial but I couldn't get the data. There are few uncertainty in my mind.
1. When I using M340 with P342020 what is the ethernet and modbus VP 5V5 r.m.c? 0.1.x
2. when I add network for ethernet it is unable to build.
3. What is the code error means for array check[2]?
I not sure what I miss out when configuring.
Early thanks for read and help in my problem.
- Labels:
-
06. EcoStruxure Control Expert
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-16 07:14 AM
your syntax for ADDM is not quite right, you have to use '0.0.3{IP Address}Tcp.mbs'. make sure Data variable array size is the same as NB, see the pictures attached.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-16 07:14 AM
your syntax for ADDM is not quite right, you have to use '0.0.3{IP Address}Tcp.mbs'. make sure Data variable array size is the same as NB, see the pictures attached.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-18 06:20 AM
Hello Anonymous,
1: r.m.c. = Rack, Module, Channel. The ethernet port of the CPU is 0.0.3
2: What's the error message in the output window?
3: Check manual https://www.se.com/nl/nl/download/document/33002527K01000/ page 42/43: 16#10 (=16 decimal) = Network module missing (probable cause is the address r.c.w. 0.1.2)
Also please set the check[4] to a defined value (>0) like 10 = timeout = 1 second). See above manual page 45
br
Sr Solution Architect (SAE Master)