Posted: 2024-07-24 12:53 AM . Last Modified: 2024-07-24 12:54 AM
How to configure Modbus tcp/ip data in M580
How to read data from modbus tcp/ip in M580. I tried ADDM & ADDMX and Read_var but not getting data.
Please guide further.
02. Modicon M580 ePAC
- Tags:
- english
Posted: 2024-07-24 09:36 PM
Are you trying to do Modbus TCP/IP communication with the M580 CPU or are you trying to communicate through BMENOC?
Posted: 2024-07-24 09:56 PM
@YONGHO-KIM I am trying to do Modbus TCP/IP communication with M580 CPU.
Posted: 2024-07-25 05:08 PM
1.Change FFB Type
AS-IS : ADDMX
TO-BE : ADDM
2. Accoding to the information you set, SLAVE is as follows.
Please check if the information is correct.
1) IP : 192.168.0.120
2) Slave ID : 14
3) Holding register
Posted: 2024-07-25 10:44 PM
@YONGHO-KIM I have tried with ADDM also but no result. I have 16 device in loop.
Posted: 2024-07-26 12:10 AM
In addition to the previous:
1: Set the timeout value (GEST parameter 3rd word) to a value other then 0 (=infinite) example 20;
2: Do this for all GEST parameters of alle communication functions;
3: INIT and (re)start the CPU
4: Check GEST parameter 2nd word for any errors (see control expert help on READ_VAR)
Posted: 2024-07-28 04:50 PM
Please refer to the attached files.
Posted: 2024-08-10 02:34 AM
For ADDM we will use IP for modbus TCP not IP of CPU ?
Posted: 2024-08-13 04:42 PM
- Do not enter the CPU's IP.
- Enter the IP of the device you want to communicate with.
Posted: 2024-08-13 09:21 PM
Dear ,
I am new for modbus TCP with M580 I have a few question as below:
1. For M580 CPU will work with ADDM or ADDMX?
2. How to create string for input ADDM or ADDMX for CPU 580?
3. In order to read data Modbus TCP we must to do both DTM and function block READ_VAR?
Posted: 2024-08-13 10:22 PM
1. Use ADDM.
2. Please refer to the attached file
ex) ADDM('{192.168.1.40}TCP.MBS')
3. Yes
Posted: 2024-08-14 06:57 AM
3. Would be a no. You do not need to use a DTM and READ_VAR at the same time. Either will work by themselves, and it would probably work better to only use one at a time.
Posted: 2024-08-16 10:50 PM
Dear
I has follow the step and I do not received any data from power meter. Can you me to check ? because I still can not found the mistake for reading modbus TCP.
Posted: 2024-08-18 04:50 PM
Please upload the PLC project file, and I will review it.
Posted: 2024-08-19 08:29 PM
What is the password?
Posted: 2024-08-19 08:35 PM
PW:Ats!@#123
Posted: 2024-08-22 02:33 AM
Dear ,
Thanks for your support now it work.
Posted: 2024-11-19 08:02 PM
Hello! Can I poll modbus rtu over tcp (moxa nport) data in the M580? Nport is running in TCP server mode. I am interested in the format of the addm or addmx string.
Posted: 2024-11-21 07:06 PM
If I use plcsim, what channel number should I specify in addm?
Posted: 2024-11-27 03:22 PM
Please try as below.
Posted: 2024-11-27 08:48 PM
Hi I would like to ask for the power meter how do you decide the slave ID as 1? doesnt modbus tcp does not require slave id
Posted: 2024-11-29 07:15 AM
The ID setting of Slave is also required in modbus tcp.
Below is an example of when the slave id is number 2 in modbus tcp.
If the M580 is the master of Modbus tcp and you want to send a signal to slave device 2, set the yellow marking to 2 and test it.