Hello,
I'm using an ION9000 and I'm setting up some data recorders using Designer tool.
I can find easily core registers (like I, U, kW...) in Power Meter Modules or HS Power Meter Module but I don't know where I can find some registers appearing in the modbus table. For sure if these registers exist in the Modbus table, they must be accessible inside Designer.
For instance, if I want to connect this register to a data recorder
where do I find this register in Designer ?
Thank you very much for you help
Link copied. Please paste this link to share this article on your social media post.
I believe it is in the Symm Comp core modules - "I Symm Comp"