Hello @james_bougie_gp
To have VIP write a value to an ION meter, the easiest way to do this is with a Distributed numeric module on VIP linked to External numeric on the ION meter. Then have External number linked to desired modbus slave module. The distributed numeric modules do have default modbus maps if you would prefer to use those.
On A side note, with PME 2020, I believe the VIP can now be configured as a modbus TCP slave.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello,
In management console, you can setup device security. I would make sure the user setup there is correct.
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @james_bougie_gp
To have VIP write a value to an ION meter, the easiest way to do this is with a Distributed numeric module on VIP linked to External numeric on the ION meter. Then have External number linked to desired modbus slave module. The distributed numeric modules do have default modbus maps if you would prefer to use those.
On A side note, with PME 2020, I believe the VIP can now be configured as a modbus TCP slave.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Charles_Murison and @james_bougie_gp
In PME 9.0, I set this up and received the following error in the "Event" Output registers of the Distributed numeric module: "Write Failed - Insufficient security to perform Distributed Control Operation"
I may need to modify something on the Data Monitor module, Distributed Numeric module or the External Numeric module or a meter or VIP security setting...
Please see screenshots below for more information. Any and all help is much appreciated!
The outputs below are:
1) Value (31) from Arithmetic module generated in the meter.
2) Value from Ext Num 4, which is linked from the VIP, arithmetic module
3) Value from Ext Num 5, which is linked from the VIP, counter module
Link copied. Please paste this link to share this article on your social media post.