Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

trying to set up a modbus export module in a VIP to send data to an ION meter

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • trying to set up a modbus export module in a VIP to send data to an ION meter
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
james_bougie_gp
Lieutenant | EcoXpert Master james_bougie_gp Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-05-15 09:53 AM

2 Likes
4
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-15 09:53 AM

trying to set up a modbus export module in a VIP to send data to an ION meter

We are trying to move data from a VIP to a BMS system.  We would like ti use modbus to do this and was thinking about using an ION meter to do this.

 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-05-16 03:24 PM

2 Likes
3
908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-16 03:24 PM

Hello @james_bougie_gp 

 

To have VIP write a value to an ION meter, the easiest way to do this is with a Distributed numeric module on VIP linked to External numeric on the ION meter. Then have External number linked to desired modbus slave module. The distributed numeric modules do have default modbus maps if you would prefer to use those.

 

On A side note, with PME 2020, I believe the VIP can now be configured as a modbus TCP slave. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-05-27 09:52 AM

2 Likes
1
889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-27 09:52 AM

Hello,

 

In management console, you can setup device security. I would make sure the user setup there is correct.

 

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-05-16 03:24 PM

2 Likes
3
909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-16 03:24 PM

Hello @james_bougie_gp 

 

To have VIP write a value to an ION meter, the easiest way to do this is with a Distributed numeric module on VIP linked to External numeric on the ION meter. Then have External number linked to desired modbus slave module. The distributed numeric modules do have default modbus maps if you would prefer to use those.

 

On A side note, with PME 2020, I believe the VIP can now be configured as a modbus TCP slave. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
dmcGPT
Lieutenant | EcoXpert Master dmcGPT Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-05-26 07:24 PM

0 Likes
2
893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-26 07:24 PM

Hello @Charles_Murison and @james_bougie_gp 

In PME 9.0, I set this up and received the following error in the "Event" Output registers of the Distributed numeric module: "Write Failed - Insufficient security to perform Distributed Control Operation"
I may need to modify something on the Data Monitor module, Distributed Numeric module or the External Numeric module or a meter or VIP security setting...
Please see screenshots below for more information. Any and all help is much appreciated!

Dist Num 1 Config.JPGDist Num 1 Input.JPGDist Num 1 Output.JPGEN4 Output.JPGMeter Security Settings.JPG

 

The outputs below are:
1) Value (31) from Arithmetic module generated in the meter.
2) Value from Ext Num 4, which is linked from the VIP, arithmetic module 
3) Value from Ext Num 5, which is linked from the VIP, counter module

Modbus slave inputs.JPGOverall.JPG

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-05-27 09:52 AM

2 Likes
1
890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-27 09:52 AM

Hello,

 

In management console, you can setup device security. I would make sure the user setup there is correct.

 

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
dmcGPT
Lieutenant | EcoXpert Master dmcGPT Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-05-28 07:07 AM

1 Like
0
886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-28 07:07 AM

I was able to resolve the write fail by:
1) In Designer, setting the Data Monitor Module source input to be the external numeric module on the meter
Data Monitor module Source.JPG
2) As you advised, in Management Console, setting up the security settings for the meter to default user, standard security and matching the password to the meter's password
Match password.JPG
3) Restarting the VIP service
4) Disabling the meter connection in management console for a minute and then enabling it
 
Thank you for your patience in helping me resolve this issue!
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc