Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

basic remote display setting question.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • basic remote display setting question.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2015-03-10 11:06 PM

0 Likes
5
2148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-10 11:06 PM

basic remote display setting question.

Hello.  Hardware Team.

it's diffcult to setting Remote-Display ION7650.

System configuration

remote display and body ION7650 connected same HUB

ION7650 IP and pc same narrow bandwidth IP address

but i can't connect through ION Setup to ION7650. how to solve this problem. thanks

Tags (2)
  • Tags:
  • display
  • remote
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-03-12 09:45 AM

0 Likes
2
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-12 09:45 AM

If the 7650 remote display is functioning with the 7650 main unit when plugged in, I would simply unconnect the remote display end of the cable temporarily and plug that into your PC.  At that point, you could change the IP Address/Subnet mask in that PC to be identical to the one in use by the remote display to see if can then communicate.  I would think the issue is with the PC and the IP Address/Subnet Mask not compatible with the one programmed into both the 7650 and the remote display in some manner.

See Answer In Context

Reply
Replies 5
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-03-11 09:52 AM

1 Like
4
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-11 09:52 AM

The 7650 remote display communicates using Modbus TCP (or Modbus RTU over a serial connection).  If the remote display is able to function with the ION7650 but you're having trouble connecting ION Setup to the same device, you should attempt to connect directly to the ION7650 using a Ethernet cross-over cable and also check that the PC IP Address/Subnet mask are similar to the one in use for the meter.  If you are able to connect using a cross-over cable but not when plugged into the switch, make sure that IP Port 7700 is open via the network switch as that is the IP port ION Setup uses to communicate ION protocol to the device (where the remote display uses IP port 502).

Reply
Anonymous user
Not applicable

Posted: ‎2015-03-12 01:51 AM

0 Likes
3
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-12 01:51 AM

thanks Robert Lee first. remote display to Body ION7650 direct connection using cross cable. second both remote display and body ION7650  connection switch hub. right??

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-03-12 09:45 AM

0 Likes
2
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-12 09:45 AM

If the 7650 remote display is functioning with the 7650 main unit when plugged in, I would simply unconnect the remote display end of the cable temporarily and plug that into your PC.  At that point, you could change the IP Address/Subnet mask in that PC to be identical to the one in use by the remote display to see if can then communicate.  I would think the issue is with the PC and the IP Address/Subnet Mask not compatible with the one programmed into both the 7650 and the remote display in some manner.

Reply
Anonymous user
Not applicable

Posted: ‎2015-03-15 10:18 PM

0 Likes
1
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-15 10:18 PM

I needs help.

i also understand IP address/Subnet mask not compatible.

main unit not reply to ping test.

configuration

remote Display unit & Main unit both connected hub.

PC IP : 192.168.10.240 / 255.255.255.0

Remote Display Unit IP : 192.168.10.20 / 255.255.255.0

Main Unit IP : 192.168.10.30

HOST PC possible ping test to remote-display,  but Main unit not reply to.

How to change the Main unit subnet mask??

when i using ION Setup, I can't connect Remote-Display Unit.

how to connect ION Setup??

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2015-03-16 09:47 AM

0 Likes
0
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-16 09:47 AM

Are you sure that the remote display is communicating with the main unit?  Does the main unit have its own integrated display or is it a transducer model (no display on the main unit).  If its the latter, did you program the main unit IP address at some point?  If not, then the issue is that the main unit is shipped with a default IP Address and the one you've entered into the remote display (the one shown for the ION device on the right hand side) is just the IP address it is attempting to connect to (not what the meter is actually configured for).

To confirm that the remote display is communicating to the main unit, if you select "Connect" button from the TCP screen, are you able to connect and view data?  If it is NOT connecting, then we need to configure the main unit IP address through some other means first (like RS-232/RS-485) or figure out what the default IP is set to.  If it is able to connect, you should be able to press the cog icon at the top of the screen and navigate to Network Setup -> General to see the IP address/subnet mask/gateway of the main unit.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore