Will appreciate your help on this. Thank you!
Link copied. Please paste this link to share this article on your social media post.
The meters which can be connected in a "5 wire system" (3 phase conductors, a neutral conductor and a separate ground conductor - the building ground) are the ones which have the GND terminal on their chassis (advanced metering and utility metering)- ION8xxx and ION7xxx.
Link copied. Please paste this link to share this article on your social media post.
Is your question about the electrical network connection or about the meter communication port (old 4-wire RS485)?
Link copied. Please paste this link to share this article on your social media post.
This is about the electrical network connection.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
This answers it. Thank you very much!
Link copied. Please paste this link to share this article on your social media post.
What about the PM8000?
Link copied. Please paste this link to share this article on your social media post.
Hi James,
The PM meters, in general, do not have exposed metallic parts therefore they do not require a grounding to protective earth (PE).