Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
I'm sure there's someone who can help me. What power quality meter would you recommend is installed on the UPS output switchboard for a data centre solution? Our prospective customer will need some convincing, so some justification would be invaluable.
Thanks
Andy
Link copied. Please paste this link to share this article on your social media post.
Todd, John,
What is the right meter if the goal is to audit the UPS and make sure it is performing as expected? Having a data record of any deviations is important so please consider setpoint configuration, event logging, and waveform logging in your answer. To help you better understand UPS performance specifications, here is an excerpt from the specification for the Symmetra MW:
Link copied. Please paste this link to share this article on your social media post.
Hi Andy - go wth a power quality meter wth the ability to capture any disturbances that the system sees at this critical point in the customer's system. I suggest an ION 7550, which can be equipped with ethernet and up to 16 digital inputs for equipment status recording if needed.