if i use PM5560 daisy chain to connect many PM5560 maybe 2 or 3 . and i want to test the commuication performence (response time in 1s)
how can i do ?
schneider have this test software or caculation tools ? thank you
Link copied. Please paste this link to share this article on your social media post.
We have tested up to 5 meters in daisy chain connection with the polling interval of 1 second.
However, the general practice for the polling interval of PM5560 will be configured as 5 seconds since the data update time is 1 second.
Regards,
Ramasamy N