Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82566members
350187posts

What are the default data logs in the PM5560

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
ken_newsome_gpt
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
1
262

What are the default data logs in the PM5560

Out of the box what does the meter store in the on-board data recorder


Accepted Solutions
Ramasamy_N
Commander Commander
Commander

Re: What are the default data logs in the PM5560

Hi Ken,

PM5560 on-board data logs will be enabled for 3 delivered energy parameters (VAh,Wh,VARh) by default with the time interval of 15 minutes in circular mode.

Customer can configure the data log settings using ION setup tool as required. Please refer the screen shot of ION setup page for available parameters below,PM5560_defaultlog.JPG

Please note that, the Demand parameters addition in progress in ION setup, will be available only on upcoming release.

Please check attached link for PM5560 user manual and refer the page number 78  for data log settings.

PowerLogic PM5500 series user manua | Download Schneider Electric

Regards,

Ramasamy.N

See Answer In Context

1 Reply 1
Ramasamy_N
Commander Commander
Commander

Re: What are the default data logs in the PM5560

Hi Ken,

PM5560 on-board data logs will be enabled for 3 delivered energy parameters (VAh,Wh,VARh) by default with the time interval of 15 minutes in circular mode.

Customer can configure the data log settings using ION setup tool as required. Please refer the screen shot of ION setup page for available parameters below,PM5560_defaultlog.JPG

Please note that, the Demand parameters addition in progress in ION setup, will be available only on upcoming release.

Please check attached link for PM5560 user manual and refer the page number 78  for data log settings.

PowerLogic PM5500 series user manua | Download Schneider Electric

Regards,