Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

SIM10M with EGX100

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • SIM10M with EGX100
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-08-20 08:15 AM

0 Likes
6
818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-20 08:15 AM

SIM10M with EGX100

Hello,

i want to use a SIM10M connected to a EGX100 to get analog inputs.

Where can i set the Modbus Slave ID of SIM10M ?

I do not find it in Installation Guide:

7250

thx

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
LazCM_175878
LazCM_175878 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-08-21 12:31 AM

0 Likes
3
762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-21 12:31 AM

Hi,

I just want to clarify ,

Once the SIM10M have been connected you can  configure using SIM configuration tool  which can be found : 

www.schneider-electric.com/products/ww/en/5100-software/5105-configuration-software/60565-simple-energy-management-solutions-sems/?xtmc=sems&xtcr=1

7254

iz in Simple Energy Management Solutions - On-site Energy Management for buildings - Installation Guide ( pag 68)

LCM

See Answer In Context

Reply
Replies 6
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2015-08-20 08:33 AM

1 Like
1
762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-20 08:33 AM

Looks like you have to connect over Virtual COM port in order to download configuration and set Slave ID register:

7249

Reply
neil_dove_varse
Ensign neil_dove_varse
Ensign

Posted: ‎2015-08-21 12:15 AM

0 Likes
0
762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-21 12:15 AM

Bojan,

You need to download a program called Sim10m Modbus Slave Programmer from Schneider

It can be found in the downloads section on the following link:

This allows all parameters to be set.

Best regards,

Neil Dove

Reply
LazCM_175878
LazCM_175878 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-08-21 12:31 AM

0 Likes
3
763
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-21 12:31 AM

Hi,

I just want to clarify ,

Once the SIM10M have been connected you can  configure using SIM configuration tool  which can be found : 

www.schneider-electric.com/products/ww/en/5100-software/5105-configuration-software/60565-simple-energy-management-solutions-sems/?xtmc=sems&xtcr=1

7254

iz in Simple Energy Management Solutions - On-site Energy Management for buildings - Installation Guide ( pag 68)

LCM
Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-08-24 04:55 AM

0 Likes
2
762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-24 04:55 AM

Hi,

sorry i only find this:

7280

is it the same to SIM configuration tool or Sim10m Modbus Slave Programmer?

Because this installs a Software called Zigbee configuration Tool

7281

Reply
LazCM_175878
LazCM_175878 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-08-24 06:08 AM

0 Likes
1
762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-24 06:08 AM

Hi,

Yes, two applications on your computer are installed. 

72697270

1. ZigBee Configuration Tool .... for EGX105Z REP100Z   and SIM6BZ, S1M10Z, SIM10M  using a USB cable

2. SIM10M Modbus Slave Programmer....   SIM10M, SIM6BZ, S1M10Z   using a USB cable

In your case you can use SIM10M Modbus Slave Programmer



LCM
Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-08-24 06:10 AM

0 Likes
0
762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-24 06:10 AM

thank you i found it

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc