Regarding V4 display in “Phasor Diagram” (ION9000)
Metering & Power Quality
Select a Country
  • EcoStruxure Power & Grid
  • Regarding V4 display in “Phasor Diagram” (ION9000)
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
Miyai
Miyai
Contributor
Posted: ‎2023-02-06 08:11 PM
1868
Regarding ION9000 “Phasor Diagram”, is there any way to customize the settings to indicate V4?
Customer wants V1, V2, V3, V4, I1, I2, I3, I4 to be displayed in Phasor Diagram.
Therefore, I am considering whether I can handle this and would like your advice.
Best regards,
Miyai
  • ION9000
Charles_Murison
Champion
Posted: ‎2023-02-08 03:37 PM
1857
Hello @Miyai ,
No setting to change the phasor diagram on meter or ION Setup to display V4. If you are using some other 3rd party application you could read information from meter's modbus map, Voltage X, H1 Angle, and Current X, H1 Angle. Magnitude information is also included in the modbus map.
Charles
Charles_Murison
Champion
1858
Hello @Miyai ,
Charles
Miyai
Miyai
Contributor
Posted: ‎2023-02-12 04:39 PM
Hello @Charles_Murison ,
Thank you for advice.
I will consult with the customer on how to respond.
Best regards,
Miyai
DanL
DanL Champion
Champion
Posted: ‎2023-02-13 11:10 AM
these same quantities are also available over the WEB api, so could be displayed in a custom web page.
Unfortunately the default web page implementation for displaying phasor diagram was hard coded with no user configuration.