Hi SEC Experts,
Two questions on the PM8000 meter:
1. Does it allow us to daisy chain othr PM8000 meters via Ethernet?
2. Does the PQ features available on the PM8000 replace the PQ functionality of the ION7650?
Please let me know.
Thank you,
Chindhu
Link copied. Please paste this link to share this article on your social media post.
Hi Chindhu
1. The PM8000 has the same dual Ethernet port function as the PM5500 series meters. So you can daisy-chain multiple PM8000 using the Ethernet connections.
2. The PM8000 does not have all of the PQ features of the ION7650 but it has a lot. It does not have flicker, but it does have disturbance direction detection and sag/swell for voltage and currents. It has 4-30 class S. It measures voltage and current harmonics and THD as per IEC 61557-12 +/- 2%.
Hope this helps,
Alana
Link copied. Please paste this link to share this article on your social media post.
Hi Chindhu
1. The PM8000 has the same dual Ethernet port function as the PM5500 series meters. So you can daisy-chain multiple PM8000 using the Ethernet connections.
2. The PM8000 does not have all of the PQ features of the ION7650 but it has a lot. It does not have flicker, but it does have disturbance direction detection and sag/swell for voltage and currents. It has 4-30 class S. It measures voltage and current harmonics and THD as per IEC 61557-12 +/- 2%.
Hope this helps,
Alana
Link copied. Please paste this link to share this article on your social media post.
Hi Chindhu,
Alana's response covered most points very well.
Here are a few other power quality features that are present on the ION7650 but not on the PM8000:
-Transient detection not supported on PM8000
-Waveform capture sampling rate of 1024 samples/cycle (PM8000 provides 256 samples/cycle today)
-IEC 61000-4-30:
-ION7650 is Class A, PM8000 is Class S as Alana mentioned
-Several parameters not supported on PM8000, including flicker, interharmonics, mains signaling and under/overdeviation
I hope this additional information helps.
David
Link copied. Please paste this link to share this article on your social media post.
Hi Chindhu -
Just to add to the others, I'll also point out the the PM8000 supports RSTP (Rapid Spanning Tree Protocol) which allows you to take advantage of the Ethernet daisy chaining to create a redundant network loop.
In short, the ION7650 is an excellent high end PQ meter, and the PM8000 is appropriate for the next level down in your metering hierarchy.
Posted: 2015-02-02 10:10 AM
Link copied. Please paste this link to share this article on your social media post.
Thank you everyone for all your help. This helps me out a lot.
Posted: 2015-02-21 07:46 AM
Link copied. Please paste this link to share this article on your social media post.
Hi
I was under the impression that PM8000 supports interharmonics in previous communication.
Can you clarify this?
Thanks
Abon
Link copied. Please paste this link to share this article on your social media post.
Hi Abon -
Interharmonics is functionality found in a high end PQ meter, such as the ION7650. The PM8000 does not support interharmonics.
Posted: 2015-07-01 07:18 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Alana,
Recently I've received inquiries for flicker detection and found PM8000 does not include that.
Since flicker is included in EN50160,I'm confused about our EN50160 support in PM8000.
Could you help to clarify?
Thanks
@Eli Liao
-Abon
Link copied. Please paste this link to share this article on your social media post.
Hi John
What is the maximum number of PM8240 meters can be connected in the Ethernet daisy chaining in redundant network loop? I knew some RSTP Supported device only support up to 15 daisy chaining.
Thanks
Jacky Lau
Posted: 2015-07-31 08:25 AM
Link copied. Please paste this link to share this article on your social media post.
Jacky,
We have not established limits for using the PM8000 with RSTP protocol, but there are some guidelines from our automation group (Industry BU) used for PLCs. In order to ensure predictable recovery time for the RSTP ring, they recommend no more than 32 devices in a daisy-chain. There are several parameters that impact this, but a key one is the Max Age parameter. The automation group recommends the Max Age parameter be set to 40. Limiting a daisy-chain to 32 devices provides some buffer to this parameter and helps ensure predictable ring recovery.
We will create some guidelines around deploying RSTP with power meters in the near future. For sure, they will be well aligned with the recommendations from our automation group to ensure interoperability of all Schneider Electric systems.
You may want to check out the "ConneXium Managed Switch Redundancy Configuration User Manual", Chapter 5, for more information on RSTP. http://download.schneider-electric.com/files?p_File_Id=689552890&p_File_Name=ConneXium-TCSESM_-TCSES...
Link copied. Please paste this link to share this article on your social media post.
Hi Alana,
Where can we find the documentation about the implementation of sag/swell for currents? I want to understand how and what this function does.
Link copied. Please paste this link to share this article on your social media post.
Hi Conrad
Exact implementation is not my expertise, but the current sag/swell detection is done through a pair of Disturbance Analyzer modules (one for sag, one for swell). If you want information on the Disturbance Analyzer module, it is described in the ION Reference.
You can also get information about the specific configuration of the current sag/swell detecting Disturbance Analyzer modules in the ION Device Template Reference compiled by the software development team.
You can get the ION Reference here:
http://www.schneider-electric.com/ww/en/download/document/70002-0290?showAsIframe=true
You can get the ION Device Template Reference here:
Hope this helps,
Alana
Link copied. Please paste this link to share this article on your social media post.
Thanks Alana. I am familiar with the ION reference so that helps a lot.
It would help a lot of the documentation gave more functional description
of the factory standard alarms so we don't need to look at the source code
to reverse engineer.
Regards,
Conrad van Rooyen
B.E. (C.S.E.) | R.P.E.Q.
P 1300 439 347 | M +61 419 410 854 | F 1800 439 347 | conradvr@hexeis.com |
www.hexeis.com
hExeis Pty Ltd
ABN: 85 134 765 576
Unit 11, 720 Macarthur Avenue Cn
Pinkenba Qld 4008
PO BOX 154
Pinkenba Qld
Australia 4008
Disclaimer: This email and all attachments ("E-mail") are confidential . If
you have received this E-mail in error please immediately contact us and
delete the E-mail and all copies. No warranty is made that this E-mail free
from viruses, errors or defects and it is the recipient's responsibility to
establish its own protection against viruses and other damage. If this
E-mail does not relate to the business of hExeis, it does not represent the
views of hExeis or related entities.
On 25 March 2016 at 00:54, Alana Clarke <
Link copied. Please paste this link to share this article on your social media post.
Hi Conrad
Thanks for the feedback about our documentation. Could you help me understand what it is that you are trying to configure for the current sag/swell detection that requires reverse engineering? We do document how to configure the voltage and current sag/swell detection using ION Setup and what the different parameters mean ("Configuring waveform recording using ION Setup", page 103 of the PM8000 user manual 7EN02-0336-01) .
We define the pickup, dropoff and nominals that need to be configured for sag/swell detection, as well as the parameters for waveform recording.

What additional information is needed for your application?
Your help in understanding how our product is used, and what information is needed, is really helpful. Thank you for your help.
cheers,
Alana
Link copied. Please paste this link to share this article on your social media post.
Hi Alana,
Thanks I hadn't found this page when doing a search for more hits on
Current Sag. As we are very familiar with the IONSETUP, ION modules and
the voltage sag/swell function I didn't read this chapter on using ION
Setup. We have implemented Current Sag/Swell functions on other IONs so
this was of interest how it had actually been implemented.
Regards,
Conrad van Rooyen
B.E. (C.S.E.) | R.P.E.Q.
P 1300 439 347 | M +61 419 410 854 | F 1800 439 347 | conradvr@hexeis.com |
www.hexeis.com
hExeis Pty Ltd
ABN: 85 134 765 576
Unit 11, 720 Macarthur Avenue Cn
Pinkenba Qld 4008
PO BOX 154
Pinkenba Qld
Australia 4008
Disclaimer: This email and all attachments ("E-mail") are confidential . If
you have received this E-mail in error please immediately contact us and
delete the E-mail and all copies. No warranty is made that this E-mail free
from viruses, errors or defects and it is the recipient's responsibility to
establish its own protection against viruses and other damage. If this
E-mail does not relate to the business of hExeis, it does not represent the
views of hExeis or related entities.
On 30 March 2016 at 01:36, Alana Clarke <
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.