Problems with clock synchronization with data loss and duplicates.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Problems with clock synchronization with data loss and duplicates.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-04-04 06:47 AM

0 Likes
9
1872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-04 06:47 AM

Problems with clock synchronization with data loss and duplicates.

Hello community

There is a client who has problems with several 7550 meters, where when reviewing the meter records it is noticed that there is data loss and like the following record the data is duplicated, where it gives an unusual value, as seen in the following image

 

Ricardo_RM_0-1712167409219.png

 


As can be seen in the record, there is a gap in the measurement that goes between 10:30 and 11:00 pm, where the data at 10:45 does not exist and the data at 11:00 gives double, that is That is, it doubles the value.

 

Reviewing the meter events, clock synchronization is just starting, as seen in the image.

This appears to be what affected the data save and is added to the data below.

 

Ricardo_RM_1-1712238280353.png

 

 

Any idea if this reason is causing this behavior or if it's something else.

 

And if it is caused by this synchronization, how can it be done so that it does not affect the data.

Thank you so much

 

Greetings

 

@Charles_Murison 

Labels
  • Labels:
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-04-08 01:35 PM

0 Likes
0
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-08 01:35 PM

Hello @Ricardo_RM ,
That sync timer is only PME. PME should have blackout times, so if meter is getting time sync inside those blackout periods, perhaps something else is time sync'ing the meters. For example ION Setup from another computer. Or there has been a change to PME that I do not know about.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 9
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-04-04 09:03 AM

0 Likes
8
1848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-04 09:03 AM

Hello @Ricardo_RM ,

The time sync is 100% the cause of the behavior you are seeing with regards to logging. The interval energy is not reset until the logging is successful, so without a log that interval the energy keeps accumulating until the next logging is successful. 

As to what can be done, does depend on what is doing the time sync to begin with. 6 seconds a quite a big time difference if meter gets time sync'd often. If using PME, there should be blackout periods where PME will not send a time sync for this exact reason. Perhaps what is sending the time sync can be configured in the same way.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-04-04 09:19 AM

0 Likes
7
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-04 09:19 AM

Hello @Charles_Murison 

Thank you very much for the response, and regarding what you mention that can be configured, where can that change be made, is it in the update interval? Which is currently at 3600000 milliseconds, that is, one hour.

Or is it in another section of the PME?

stay tuned

Thank you so much

Greetings

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-04-04 10:10 AM

0 Likes
6
1839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-04 10:10 AM

Hello @Ricardo_RM ,


That setting sounds a lot like a PME setting. The blackout interval is hard coded into PME and not configurable. If PME is still sending out a time sync inside the black out period this would be a PME behavior and you would need to contact PME tech support to troubleshoot.

 

6 seconds time difference in 1 hour is huge, may be something else that needs to be investigated. can you share clock's settings?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-04-04 01:20 PM

0 Likes
5
1830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-04 01:20 PM

Hello @Charles_Murison 

 

I share the clock configuration with you.

 

Ricardo_RM_0-1712261789206.png


A relevant fact that I discussed with the client is that this configuration is the same for the other meters that have been installed and do not present the same error, the other models are 7650, ION9000, ION8650 and Access 9600. It only happens with the 7550

 

Regarding the PME, it has already been reviewed and as you mention there are no problems, the PME does keep the following record correctly as seen in the image

 

Ricardo_RM_1-1712261905987.png


The PME on the missing record assigns a 0 and the next value if it saves the data correctly.

 

But the drawback that the client has is that it is a Utility, and it uses a system that takes the values ​​directly from the meter to bill, and since the data after the failure is a very high and erroneous value, it is a problem since it is being billed. more than was actually achieved.

 

So we would like to know if there is any configuration to be able to correct this problem, if there is any blockage or if we should schedule the meter synchronization at a time that does not affect data collection.

 

Regards,

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-04-04 02:04 PM

0 Likes
4
1826
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-04 02:04 PM

Hello @Ricardo_RM ,

"would like to know if there is any configuration to be able to correct this problem" The only thing I could suggest is if you are only using 1 kind of time sync (ION, NTP etc.) set the source to that specific protocol. Other than that not much you can configure on the meter you are not already doing.

 

"should schedule the meter synchronization at a time that does not affect data collection." Yes! I would recommend do not synchronize meter 1 minute before and after :00, :15, :30, :45.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-04-05 01:41 PM

0 Likes
3
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-05 01:41 PM

Hello @Charles_Murison 

 

Thank you very much, to clarify, when you mention “configure the source in that specific protocol” do you want to mention that in the clock configuration you change where it says ETHERNET to Ethernet-ION or similar?

 

Also, when you mention "Yes! I would recommend not syncing the meter 1 minute before and after :00, :15, :30, :45." This means manually or there is a section or parameter in the meter settings for it to sync automatically.

 

Greetings.

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-04-05 02:45 PM

0 Likes
2
1779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-05 02:45 PM

Hello @Ricardo_RM ,

 

There is no setting on the meter to say when the meter will time sync. The time sync is initiated by what is time syncing the meter. (NTP being the exception). 

"change where it says ETHERNET to Ethernet-ION or similar?" correct

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-04-08 12:17 PM . Last Modified: ‎2024-04-08 12:18 PM

0 Likes
1
1737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-08 12:17 PM

Hello @Charles_Murison 

 

Thank you very much for the answers, I am going to notify the client that what can be done is modify the type of synchronization.

 

I would also like to ask a question, as seen in the image of this spec sheet that can be viewed from the Management Console, is there a sync timer, does modifying this option affect the meter or is it only for the PME?

 

Ricardo_RM_0-1712603853385.png

 

 

 

Greetings

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-04-08 01:35 PM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-04-08 01:35 PM

Hello @Ricardo_RM ,
That sync timer is only PME. PME should have blackout times, so if meter is getting time sync inside those blackout periods, perhaps something else is time sync'ing the meters. For example ION Setup from another computer. Or there has been a change to PME that I do not know about.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of