PowerTag A9MEM1521/22 measurements

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa453448_brid
Ensign Ensign
Ensign
0 Likes
5
869

PowerTag A9MEM1521/22 measurements

Hi Guys,

 

I can't find information about the measurement capabilities of the N-Terminal of PowerTag A9MEM1521/22, are the same as the phase-Terminal?. We're planning to use these PowerTag references for a 2-phase system, any other ideas? is better to use 2 A9MEM1520 instead?

 

Thanks!!! 🙂

 

 

Tags (1)

Accepted Solutions
Romain_Polette
Sisko Sisko
Sisko

Re: PowerTag A9MEM1521/22 measurements

Hello @sesa453448_brid , 

 

Can you precise your architecture ?
N Terminal for any PowerTag Sensor has no CT. It is only used as a Voltage Reference so you cannot monitor any current on the Neutral.

If I understand your system will be : N, L1, L2 (No L3 ?). If you plan to use A9MEM1521/22 => it means that you have Acti 9 MCB. Can you give me the commercial ref of the breakers ?

Depending on your answer I may suggest you some configuration.


Thanks.

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France

See Answer In Context

Tags (1)
5 Replies 5
Romain_Polette
Sisko Sisko
Sisko

Re: PowerTag A9MEM1521/22 measurements

Hello @sesa453448_brid , 

 

Can you precise your architecture ?
N Terminal for any PowerTag Sensor has no CT. It is only used as a Voltage Reference so you cannot monitor any current on the Neutral.

If I understand your system will be : N, L1, L2 (No L3 ?). If you plan to use A9MEM1521/22 => it means that you have Acti 9 MCB. Can you give me the commercial ref of the breakers ?

Depending on your answer I may suggest you some configuration.


Thanks.

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
Tags (1)
marco_arias_ssm
Cadet
0 Likes
3
840

Re: PowerTag A9MEM1521/22 measurements

Hello Romain

I want to conect A9MEM1570 in L1-L2-L3 system (No N). Will be any problem if i no conect the N terminal of powertag?

 

Regards

Tags (1)
Romain_Polette
Sisko Sisko
Sisko
0 Likes
2
835

Re: PowerTag A9MEM1521/22 measurements

Hello @marco_arias_ssm , 

 

If you have a 3ph system without Neutral : it is more recommended to connect a A9MEM1573.

 

If you use the A9MEM1570 and if your system is balanced : your measurement precision will not be affected. But.... what are you going to do with the N pin of the PowerTag 1570 ?

 

Keep in mind that 1570 is dedicated for 3P+N unbalanced system. Neutral will improve the precision of the Power measurement.

 

Regards.

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
Tags (1)
marco_arias_ssm
Cadet
0 Likes
1
831

Re: PowerTag A9MEM1521/22 measurements

Thanks Romain

I ask about the A9MEM1575 reference. I only see the A9MEM1570 in stock.

 

Regards

Tags (1)
Romain_Polette
Sisko Sisko
Sisko

Re: PowerTag A9MEM1521/22 measurements

Hello @marco_arias_ssm , 

 

A9MEM1575 does not exists. I mentioned A9MEM1573 in my previous comment.

 

Please refer to the selection guilde.

Regards.

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
Tags (1)