Good day to all,
We recently got wind of the above problem that the PowerLogic PM5560 / 5561 meters refuses to store the subnet mask and gateway IP despite deliberate attempts to set them in the ethernet port configuration page via the meter's front display. We conducted a simple test trying to set the meter to the following configuration,
IP Address : 169.254.000.110
Subnet Mask : 255.255.000.000
Gateway IP : 169.254.000.001
After saving, and returning to the ethernet configuration page, we observed the following,
IP Address : 169.254.000.110
Subnet Mask : 000.000.000.000
Gateway IP :000.000.000.000
Has anyone encountered the same error elsewhere? Appreciate everyone's time to check on this as it may become a widespread customer satisfaction issue.
KK Tan
Link copied. Please paste this link to share this article on your social media post.
Hello Kuan Khoon Tan,
How about the IP address? It does not reset as well?
You might want to wait a couple of seconds (7-8sec) after you modify the Ethernet configuration and before returning to the page where you actually save the changes. and you save it. After 7-8 seconds, recheck the Ethernet settings.
Let me know if it works for you.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2016-12-15 12:12 AM
Link copied. Please paste this link to share this article on your social media post.
Hello Kuan,
Please try after adding new settings to power off the meter and then power on.