Power Quality Events - ION Meters

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Power Quality Events - ION Meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
528
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
139
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Gavin_Bryson
Commander | EcoXpert Master Gavin_Bryson Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-07-07 09:37 AM

0 Likes
5
3230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-07 09:37 AM

Power Quality Events - ION Meters

Hi,

 

We have installed ION9000s, ION7650s and PM8240s on a customer's UK site and German site. Some PQ events have occurred, transients, interruptions, sags, swells etc.

 

However, when I review the logs on the meters via PME, some of the meters stopped logging events maybe a month or 2 months ago in some cases.

 

Does anyone know why this would be occurring? Do I have to do something with the ION meter's onboard memory? I thought older PQ events were overwritten with new PQ events whenever memory was at capacity?

 

Would anyone be able to offer any advice?

 

Kind regards,

 

Gavin

Labels
  • Labels:
  • ION9000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-07-13 02:22 PM

1 Like
0
3159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-13 02:22 PM

Hello @Gavin_Bryson ,

 

One item to watch out for when upgrading meters, the default template that is shipped with firmware file does not have sag/swell enabled. If user had meter configured, did not save the template before upgrading and just used the default template, the sag/swell module after upgrade will be the default state (disabled).

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
GordErickson1
GordErickson1
Cadet

Posted: ‎2021-07-07 11:29 AM

0 Likes
1
3226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-07 11:29 AM

I would start by checking the waveform/data recorders settings. They could be set to STOP-WHEN-FULL rather than CIRCULAR.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-07-07 11:46 AM

1 Like
2
3223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-07 11:46 AM

Hello @Gavin_Bryson ,

 

My be good to describe what you mean by "meters stopped logging events" For example, no new records in the meter's event log, or events in the event log but no waveforms, Waveforms but no event data, sag/swell logged details but no event. Would also be good to know a bit of history of the meters, did they have firmware upgrades and/or new templates pasted?

 

Some items to check

a) Setpoints for the events are correct, eg, nominal voltage, voltage modes etc

b) Event priority in modules is above eventlog threshold (default is 5)

c) Module is enabled, some modules have both a setup register and/or input that could be linked to activate/deactivate a module

 

If pasting a template/framework onto a meter is it possible 1 or more settings got changed that would deactivate the module in question.

 

For more exact troubleshooting for a specific meter I would recommend contacting technical support (se.com->support->contact support)

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Gavin_Bryson
Commander | EcoXpert Master Gavin_Bryson Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-07-13 12:43 AM

0 Likes
0
3172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-13 12:43 AM

Thanks @GordErickson1 I will check how the Data Recorders have been configured

Tags (1)
  • Tags:
  • english
Reply
Gavin_Bryson
Commander | EcoXpert Master Gavin_Bryson Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-07-13 12:46 AM

0 Likes
1
3170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-13 12:46 AM

Thanks @Charles_Murison , apologies for the limited information. We haven't modified any frameworks on the meters. The firmware would have been updated with the recommended firmware updates circulated last year.

 

The information was shared with me in a Teams call, visibility was very poor. I will be connecting remotely sometime this week and hope to get a better insight on what is happening with the meters.

 

Kind regards,

 

Gavin

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2021-07-13 02:22 PM

1 Like
0
3160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-13 02:22 PM

Hello @Gavin_Bryson ,

 

One item to watch out for when upgrading meters, the default template that is shipped with firmware file does not have sag/swell enabled. If user had meter configured, did not save the template before upgrading and just used the default template, the sag/swell module after upgrade will be the default state (disabled).

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore