Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
While running some tests on a custom ION7550 framework I observed that the "position" of the calibrated pulser module is not getting reset despite having done a master reset on the device.
I would assume the master reset clears out everything (logs, energy, demand, min, max, ect.). But it appears the position on these modules is always remembered.
I am outputting a kWh pulse on R1 (1 kWh= 1pulse -> Kt=1000. I do a master reset, energy registers reset. However when say 0.45kWh accumulates, the module pulses the port.
Is this normal intended behavior?
Link copied. Please paste this link to share this article on your social media post.
Matthew,
Did you do resetting when there was load ? If so one second after reset was done you will have energy accumulated for sure.
Yut