Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 downgrade to 001.000.057

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 downgrade to 001.000.057
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
Marcos_Augusto
Marcos_Augusto Contributor
Contributor

Posted: ‎2016-11-22 10:23 AM

0 Likes
4
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-11-22 10:23 AM

PM8000 downgrade to 001.000.057

A customer has reported a problem when trying to downgrade the 001.003.000 PM8000 FW to 001.000.057.

When doing this he got the attached screen.

I just found a PM8000Signature.cer file, but I am not sure if this file is related to the described issue and how to proceed to succeed on downgrading the PM8000 FW.

Just in case, the purposes of downgrading the meter are two:

1) The customer has many other PM8000 fw 001.000.057 units in the same substation and would like to keep all of them in the same firmware version.

2) According to him, the IEC61850 communication when using firmwares 001.002.0014 and 001.003.000 did not work as expected.

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2016-11-24 09:41 AM

0 Likes
3
2341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-11-24 09:41 AM

Unfortunately all ION firmware now contain a new cyber-security feature where the firmware must now be digitally signed to be accepted for upgrade (this is to prevent sending firmware which has been modified).  As such ION Setup will no longer allow the downgrading of this type of firmware (even circumventing the software block would still have the error of downloading the entire firmware file only for the device to reject it at the end).

Since the problem is not related to the newer firmware, the best course of action is to first attempt to determine why the newer firmware is not properly functioning with IEC61850 rather than attempting to use older firmware.  I would suggest opening up an incident with Tech Support so they can investigate what the issue is that is preventing the newer firmware from communicating properly on IEC61850.

Reply
Marcos_Augusto
Marcos_Augusto Contributor
Contributor

Posted: ‎2016-11-24 09:57 AM

0 Likes
2
2341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-11-24 09:57 AM

Hi, Robert.

Firstly, thanks for your comments and clarification.

I totally agree with you on not downgrading the firmware.

Actually, I have tested version 001.003.001 with Matrikon OPC IEC61850 Server by myself and it is working fine. The problem reported by the customer is kind of compatibility issue with PACIS system.

I have been notified about this issue only last week, but the problem is far older and the customer has no more time for tests or whatever. They are more likely to change the whole system protocol to DNP3, instead. It is gonna be a lot of work, but probably faster than digging the PACIS compatibility problem.

I just tried to downgrade from 001.003.001 to 001.002.014 right now and it worked fine. No error messages at all.

Anyhow, I could not do the same from 001.001.014 to 001.000.057.

Thanks.

Reply
Sanjeet_Sahota
Sanjeet_Sahota Mentor
Mentor

Posted: ‎2016-11-30 02:54 PM

0 Likes
1
2341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-11-30 02:54 PM

Hi Marcos,

Digging into my e-mail history, we also faced a similar scenario on PACis HMI and the ION8650.  The protocol implementations are nearly identical between platforms and we had faced a similar issue with PACis.  I suggest you sync up with Novianti and Parlindungan Sitorus out of India for what their resolution was for a similar problem they faced.   They may have found a work around that could be implemented for the PM8000.


Regards,

Sanjeet

Reply
Marcos_Augusto
Marcos_Augusto Contributor
Contributor

Posted: ‎2016-12-01 06:46 AM

0 Likes
0
2341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-12-01 06:46 AM

That's great! Will check with them.

Thank you very much, Sanjeet.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.