Hi, the new IEEE STD 519-2014 has specified harmonic measurement compliance. I understood that PM8000 series is complied with IEC 61000-4-30.
Is the PM8000 able to comply to IEC61000-4-7 or any plans to make it to comply to that standard?
The only meter that can comply both IEC61000-4-30 and IEC61000-4-7 is ION7650 series, am I right?
Link copied. Please paste this link to share this article on your social media post.
With respect to the IEC 61000-4-7, please ref. to the attached technical note "4-30 compliance and ION meters" -> page 7.
With respect to the IEEE 519 compliance, please see Tom Stevenson 's reply here: https://community.se.com/message/69309#69309
According to the existing documentation, the meter is compliant with IEEE 519.
Regards,
Victor
Link copied. Please paste this link to share this article on your social media post.
Hello,
Please note that the PM8000 complies with IEC 61000-4-30 Class S requirements which are different compared with the requirements foe a Class A meter.
Is there some requirement that you think the PM8000 is not meeting - with respect to IEC 61000-4-30 Class S requirements (which also incorporates IEC 61000-4-7 requirements - see for eg. "Voltage harmonics" -> "Measurement method" -> Class S)?
I hope it helps,
Regards,
Victor
Link copied. Please paste this link to share this article on your social media post.
VICTOR MARINCUS, I'm not sure what is the different between Class S and Class A meter as I don't have IEC 61000-4-30 standard.
Here's the requirement from IEEE STD 519-2014 on the instrument to measure the harmonics (see the images below).
My questions:
1) Can PM8000 perform these requirements (4.1 - 4.3)?
2) Are you saying that that PM8000 complies to IEC 61000-4-7? If yes, can we include that in the standard compliance list?
Link copied. Please paste this link to share this article on your social media post.
With respect to the IEC 61000-4-7, please ref. to the attached technical note "4-30 compliance and ION meters" -> page 7.
With respect to the IEEE 519 compliance, please see Tom Stevenson 's reply here: https://community.se.com/message/69309#69309
According to the existing documentation, the meter is compliant with IEEE 519.
Regards,
Victor