Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

PM800 Comms options with PM8ECC and PM8RDA

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM800 Comms options with PM8ECC and PM8RDA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Anonymous user
Not applicable

Posted: ‎2015-07-07 02:19 AM

0 Likes
2
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-07 02:19 AM

PM800 Comms options with PM8ECC and PM8RDA

Is there any document anywhere that describes the communications option that can be configured with the various PM800 options, the PM800 has an RS485 port, the PM8ECC adds Ethernet and another RS485 port, then if the meter is without display a PM8RDA can be added, what we require is a document or diagram describing what would be slave and master ports in the various configurations, this has come about as we have had requests to connect to two separate masters, we have conflicting information direct from UK technical support and what we are reading on FAQ's, for example:


Issue:
PM800 Series meters without the Ethernet Communications card (PM8ECC) and without the remote display adaptor (PM8RDA) have only one communication port (Comm 1) which is a 2-wire RS485 Port. When adding PM8ECC and remote display adaptor, two additional comm ports are included with these modules and they can be used in 2-wire or 4-wire mode.

When should each comm port be used? Can all 3 RS485 comm ports be used when adding a PM8ECC to a Series 800 Power Meter (PM800) with a remote display adapter?

Product Line:
PM800, PM820, PM850, PM870

Environment:
Serial/Ethernet Communication
RS-485 Communication

Cause:
There are three Serial Comm ports on a PM800 when PM8ECC and PM8RDA Modules are installed. A user may not know which comm port to use depending on the communications requirement.

Resolution:
The following serial communications ports are available on a PM800 when there is a PM8ECC and PM8RDA installed:

1. The PM800 series meter base unit has one 2-wire RS-485 port (Comm 1). RS-485 Slave Port
2. The PM800 Remote Display Module has one 4-wire RS-485 port (Comm 2). RS-485 Slave Port
3. The PM800 Ethernet Communications Card (PM8ECC) one 4-wire RS-485 port (Comm 3). RS-485 Master Port

When should each port be used?

1. The base unit 2-wire RS-485 port should be used to communicate directly with a PM800 if you have a 2-wire RS-485 daisy chain.
2. If you have a PM800 with a Remote Display module and you need to connect the PM800 to a 4-wire RS-485 daisy chain, use this communications port on the Remote Display Adapter. For a 2-wire RS-485 daisy chain you can use either port.
3. If you have a PM800 with a PM8ECC and you intend to use the Ethernet Communication card as a gateway, you will need to connect the downstream RS-485 wiring to the port on the Ethernet Communication card. This port is configurable for 2-wire or 4-wire via dip switches.
4. When the PM8ECC is added to a PM800 Meter with a remote display adapter (PM8RDA), the RS485 comm port 2 on the remote display adapter becomes disabled. Only two RS485 ports (Comm 1 and Comm 3) can be used simultaneously. COM 1 is a RS-485 Slave Port and COM 2 is a RS-485 Master port.
5. When the remote display adapter is added to a PM800 Meter without the PM8ECC, Comm 1 and Comm 2 can be used simultaneously. Both ports will require a different RS485 address (Device ID).

http://www2.schneider-electric.com/sites/corporate/en/support/faq/faq_main.page?page=content&country...

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
sesa373725
sesa373725 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-03-10 12:32 PM

0 Likes
1
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-10 12:32 PM

Hi,

If you have remote display module on PM8XX, can you use 2-wire connection. For instance, one can jumper + and - terminal on RS-485 connection on remote display module. I did tried that and it did not work. Do you need to use 4 wire to 2 wire converter?

Reply
Yu_Diao
Commander Yu_Diao Commander
Commander

Posted: ‎2016-03-10 06:12 PM

0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-03-10 06:12 PM

Oun,

If there is no PM8ECC installed on the same PM8 meter, you should be able to use the PM8DRA's RS485 port in 2-wire connection by jumping both Tx+/Rx+ and Tx-/Rx-. The last time I used both com1 and com2 in 2-wire connection on PM8 was about half month ago, and these meters worked fine.

Regards,

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of