PM3255 Active energy into load

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa250204
Ensign
Ensign
0 Likes
4
405

PM3255 Active energy into load

Hi all,

I have one problem using PM3255 on PME 7.2.1.

I don't have any informations about active energy into the load. I have standard log for Active out, Reactive in and out and Apparent in and out.

Also on Load report and tabular report I dont have data for Active energy. Still I have date for total active energy in and out before last reset.

Do I need to active it manually on meter? It is 300 km from my office, and I will be glad to solve it remotly.

4 Replies 4
ganesh_azzo_com
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
3
329

Re: PM3255 Active energy into load

Hi Mario,

    

The first thing you can cross verify is , In PME 7.2 Active Energy into load is not default checked in MDI. Kindly try to tick the energy Into Load and see if you see data logging if not then you have to see in the meter  setup---->Log----> Energy Into load is “Enabled “.


JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
2
329

Re: PM3255 Active energy into load

You cannot enable the onboard flex log or configure it remotely. Normally this is where that measurement comes from.  Instead, just tick it in the MDI.

sesa250204
Ensign
Ensign
0 Likes
1
329

Re: PM3255 Active energy into load

Thanks for the answer.

I did it through MDI, Active power into the load was not automatically checked.

One more question, how can we enable Load interval logging for day, week and the month?

Hal_Etheridge
Janeway Janeway
Janeway
0 Likes
0
329

Re: PM3255 Active energy into load

Just change the logging interval in the MDI for whatever period you want.  By default it should be logging every 15 minutes but this can easily be changed to whatever interval you wish.  The SW logging is controlled (in the driver) by a periodic timer with the same capability as the VIP (or the ION devices).