Hello, how are you all?
I'm making an application with an M580 and a P5F30 relay in ModbusTCP communication. I would like to know if there is any control block ready to be used in the PLC logic. Grateful
Link copied. Please paste this link to share this article on your social media post.
I think that Generic Modbus DTM will be suitable but please check that the communication on P5 side is active
Link copied. Please paste this link to share this article on your social media post.
Hello Afvanin,
you have two methods,
the first approach is to use DTM and add a Modbus device on DTM browsers, then add a request to pull "Read" the data.
The second approach , uses one of communication blocks like Read_Var Block to read the data from P5 Relays , for more details please check the attached pdf
Link copied. Please paste this link to share this article on your social media post.
Hi @Mnabil.
Is there any specific DTM for the P5, or should I use the Generic Modbus DTM? Because I believe that doing it through the DTM, it is simpler to carry out the logic, instead of using READ_VAR.
Thank you very much!