Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

P3U30 energy reading from modbus connection

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • P3U30 energy reading from modbus connection
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
526
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Mentor
Ensign Mentor
Ensign

Posted: ‎2023-02-28 10:13 AM

0 Likes
5
3570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-28 10:13 AM

P3U30 energy reading from modbus connection

Hello,

 

I am connection a schneider protection relay P3U30 with a Siemens SCADA (WinCC) through modbus tcp.
As per communication setting, I can read values like voltage, current, power ect. But I have a problem with reading of the Energy values (adress 402026).

Energy calculation mode is set to Fundam, is that ok?

In the Wincc, tag setting is: "signed 32-bit value" - "LongToSignedDWord" address: 3x402026.

Here I can read some values, but they are giving me rong measurment and is not the same value as it is in the relay. (reading from eSetyp Easergy Pro/measurments/energy/Exportet energy.
I tried to read this address from "modbus poll" software with different addresses and types, but never get the right number.

 

Please suggest me how to solve this?

 

Thanks and best regards.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
peer.mydeen
Lieutenant peer.mydeen Lieutenant
Lieutenant

Posted: ‎2023-02-28 08:44 PM

0 Likes
4
3560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-28 08:44 PM

Hi,

The format you calculating is wrong

 

The format is 

U48-M10k-21-65

U48-M10k-21-65

A 48-bit unsigned value returned in three consecutive 16-bit registers. R3*10,000^2 + R2*10,000 + R1, where R3 is the last register and R1 is the first register. Each registers range is 0 to +9,999

See Answer In Context

Reply
Replies 5
peer.mydeen
Lieutenant peer.mydeen Lieutenant
Lieutenant

Posted: ‎2023-02-28 08:44 PM

0 Likes
4
3561
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-28 08:44 PM

Hi,

The format you calculating is wrong

 

The format is 

U48-M10k-21-65

U48-M10k-21-65

A 48-bit unsigned value returned in three consecutive 16-bit registers. R3*10,000^2 + R2*10,000 + R1, where R3 is the last register and R1 is the first register. Each registers range is 0 to +9,999
Reply
Mentor
Ensign Mentor
Ensign

Posted: ‎2023-03-01 01:12 PM

1 Like
3
3548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-01 01:12 PM

Thank you MpKpeer,

 

As we do not have any option in WinCC for 48-Bit Tag. I did it as you suggested by creating 3 tags 16-bit and then with a script I did the calculation and sent the result in another tag 64-Bit.

 I can read the correct value now.

Reply
Nhuautomation
Nhuautomation
Cadet

Posted: ‎2023-11-13 01:47 AM

0 Likes
0
3154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-13 01:47 AM

hello i cannot read device p3u30 to PLC s7-1200 by Modbus TCP

I test by software Modbus Poll then i see address but i convert the PLC no read

Can you help me

 

Reply
Nhuautomation
Nhuautomation
Cadet

Posted: ‎2023-11-13 01:55 AM

0 Likes
1
3154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-13 01:55 AM

hello,

I cannot read register device p3u30 to device s7-1200. i read the document the register 402009 but in the PLC I cannot see.

I test by software Modbus Poll then  I see register device P3u30 repply

Please suggest me how to solve this?

Thanks and best regards.

Reply
Mentor
Ensign Mentor
Ensign

Posted: ‎2023-11-20 05:38 AM

0 Likes
0
3126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-20 05:38 AM

Hello,
Have you tested your PLC program with other devices? I means is the PLC configurated correctly?
In the PLC, the modbus address is one number bigger. So please try the address 402010 with data length 2.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore