Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Need CT Sensor suggestion for EM6400NG+

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Need CT Sensor suggestion for EM6400NG+
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-10-04 06:30 AM

1 Like
6
2649
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-04 06:30 AM

Need CT Sensor suggestion for EM6400NG+

Hello Everyone,

 

I am testing the EM6400NG+ energy meter for energy logging, In my setup, I used SCT010 20A:20mA CT and 10A variable load. To start I started testing with a single phase supply and I am able to see voltage measurement on the device, I tried many combination setting to get the measurement of current, but still device shows zero reading. I am confused as to do I am using the right CT sensor or the wrong configuration. Any help will be appreciated.

 

Thanks in Advance.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-10-17 10:28 PM

0 Likes
3
2583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-17 10:28 PM

Hello @Anonymous user 

 

EM6400NG+ supports only the Ip/5A or Ip/1A secondary current CTs, the SCT010 is low voltage output CT and the EM6400NG+ will be able to measure the output of SCT010 CT. 

 

You can test with any METSECT5xxxxx CT references listed from the Powerlogic catalog. 

https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_%28Web%2...

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-10-18 03:18 AM . Last Modified: ‎2022-10-18 03:21 AM

0 Likes
1
2568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-18 03:18 AM

Hello Kirankumar, 

 

Please confirm the CT secondary output current, if it 1A when the primary current 100A is applied. (no information available is web for this CT). 

If yes, you can connect this CT with EM6400NG meter and configure the CT primary as 100A and secondary as 1A. 

 

Please share the injected and measured current values if you see any difference. 

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-10-17 10:28 PM

0 Likes
3
2583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-17 10:28 PM

Hello @Anonymous user 

 

EM6400NG+ supports only the Ip/5A or Ip/1A secondary current CTs, the SCT010 is low voltage output CT and the EM6400NG+ will be able to measure the output of SCT010 CT. 

 

You can test with any METSECT5xxxxx CT references listed from the Powerlogic catalog. 

https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_%28Web%2...

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-10-18 03:02 AM

0 Likes
2
2571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-18 03:02 AM

Hello @Ramasamy_N 

 

Thanks for the reply, you said I am proceeding to 1p/1A  to test it and below is the CT I found similar. Can you please confirm the same https://robu.in/product/yhdc-sct-024ts-100a-1a-split-core-current-transformer/?gclid=Cj0KCQjwnbmaBhD....

 

Thanks & Regards,

KISHANKUMAR J

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-10-18 03:18 AM . Last Modified: ‎2022-10-18 03:21 AM

0 Likes
1
2568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-18 03:18 AM

Hello Kirankumar, 

 

Please confirm the CT secondary output current, if it 1A when the primary current 100A is applied. (no information available is web for this CT). 

If yes, you can connect this CT with EM6400NG meter and configure the CT primary as 100A and secondary as 1A. 

 

Please share the injected and measured current values if you see any difference. 

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-11-12 12:57 AM

0 Likes
0
2376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-12 12:57 AM

Hii Ramasamy,

 

Thank you for your support and suggestions for the query, The configuration setting has been found on youtube, and for measurement results, I will share you in some time.

 

Regards,

KISHANKUMAR J

Tags (1)
  • Tags:
  • english
Reply
sanjay16008
sanjay16008
Explorer

Posted: ‎2026-03-27 06:03 AM

0 Likes
1
571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-27 06:03 AM

How to communicate with PC of EM6400NG+ meter

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-03-30 09:36 AM

0 Likes
0
568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-03-30 09:36 AM

Hello @sanjay16008 ,

 

Please fere to user Manual
https://www.productinfo.schneider-electric.com/em6400ng/5af9a18446e0fb00011e3318/EM6400NG%20User%20M...

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore