Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Ion9000 communication failure after security updates

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Ion9000 communication failure after security updates
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Oz_Ba
Oz_Ba
Troubleshooter

Posted: ‎2022-09-29 04:27 AM

1 Like
4
4538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-29 04:27 AM

Ion9000 communication failure after security updates

Hi,

 

I am having trouble reading data from Ion9000 device after client's IT department performed security policy updates.

 

PME 2020 is running with only one device connected directly using ethernet. It is Ion9000. 

Measurements from other 100+ devices are loaded into PME's SQL using ETL and this part is just fine.

 

Management console shows failure status for Ion9000 as you can see from the image attached.

 

No modifications to PME were made. 

Valid license is applied for high-end device.

 

I have had similar issue earlier and I managed to solve this by removing Ion9000 device from PME and then following steps described in this article:  Could not write to Event log pipeline in Alarm Service." after upgrading to PME 2020 | Schneider Ele... Then, I added Ion9000 again with new name and it worked.

 

Ion9000 is available through network using web browser or IonSetup v3.2 tool.

I also recorded data traffic on port 7700 between PME's and Io9000's IP address.

 

 

I am sure this has to be related to user account suspension and changes IT guys made after certain cyber-attacks.

 

Any suggestion is appreciated.

 

 

 

 

 

 

 

 

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Oz_Ba
Oz_Ba
Troubleshooter

Posted: ‎2022-10-13 05:27 AM

0 Likes
0
4382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-13 05:27 AM

Hi,

 

This was a cyersecurity issue.

 

Looks like new AI-based security solution (which I am not going to specify) blocked execution of siteserver.exe. 

I was confused by the fact that SiteServer service reported no issues.

 

@Charles_Murison thaks for your replies.

 

 

 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-10-03 02:12 PM

0 Likes
3
4465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-03 02:12 PM

Hello @Oz_Ba ,

 

The failure state is somewhat generic of a message and not much to go on for troubleshooting. It could be that some services were started in incorrect order or it could be that the port to the meter is blocked or could mean something between ION components are failing (DCOM). First step would be to stop all ION services (not just automatic ones). There are 2 services that are not automatic but start when ION Network Router service is started. If either of these services are started before ION Network Router service this can cause problems within PME.

 

If restarting the services do not help, likely you will want to work with Tech support to start a case and troubleshoot.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Oz_Ba
Oz_Ba
Troubleshooter

Posted: ‎2022-10-04 01:36 AM . Last Modified: ‎2022-10-04 01:40 AM

0 Likes
2
4448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-04 01:36 AM

@Charles_Murison 

Thank you for your reply.

 

I am aware of ION services startup order, I tried restarting services in regular order many times. It did not give results.

I am able to use Ion Setup tool with no issues, I can read Realtime data, setup parameters, etc. That means ports are not blocked, right?

I also noticed that there is traffic present an port 7700 all the time. Looks like communication services are reading data from ION9000 but something is stuck between services.

 

I will definitely have to talk to tech support.

 

Regards,

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-10-04 08:28 AM

0 Likes
1
4438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-04 08:28 AM

Hello @Oz_Ba 

 

If ION Setup is able to talk to the device, that does indicates that ports are not blocked. Would need to understand what traffic PME is sending to confirm if this a concern or not. Very likely tech support is your best option moving forward.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Oz_Ba
Oz_Ba
Troubleshooter

Posted: ‎2022-10-13 05:27 AM

0 Likes
0
4382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-13 05:27 AM

Hi,

 

This was a cyersecurity issue.

 

Looks like new AI-based security solution (which I am not going to specify) blocked execution of siteserver.exe. 

I was confused by the fact that SiteServer service reported no issues.

 

@Charles_Murison thaks for your replies.

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore