Ion 7650 with EN50160 modbus communication

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Ion 7650 with EN50160 modbus communication
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa389533_brid
sesa389533_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-06-13 06:07 AM . Last Modified: ‎2020-04-22 01:16 AM

0 Likes
3
1230
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-13 06:07 AM

Ion 7650 with EN50160 modbus communication

Is it possible to have a modbus alert when a disturbance start (EN50160) ? If not, how can i have this informations ?

 

We would like to add this informations in our supervision.

 

I can see the events with ION Setup. (cf .txt).

 

Other thing, this is the first time that i use an ION 7650, Should i update it ?

Attachments
Event Log for MJ-1612A071-05.txt.zip
Labels
  • Labels:
  • ION Setup
Tags (2)
  • Tags:
  • en50160
  • ion7650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-06-13 10:17 AM

0 Likes
2
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-13 10:17 AM

Hi Francois

The ION7650 has many Modbus registers that detail EN50160 values.

These registers are listed in the Modbus Protocols and Register list pages 29 to 34, available from the website here:

http://www.schneider-electric.com/en/download/document/70022-0124-01/

Your meter's firmware is quite recent, there is a newer version V410 if you want to upgrade, available from the website here:

firmware: http://www.schneider-electric.com/en/download/document/7650V410/

templates: http://www.schneider-electric.com/en/download/document/ION7650_v410_Templates/

I do not know what you mean by a Modbus alert, however you can configure the ION7650 to send email alerts when an event occurs. You can use Advanced mode of ION Setup to configure this.

You can access a technical note describing how to send alerts from the website:

http://www.schneider-electric.com/en/download/document/70072-0125-02/

And you can get information about ION modules (including the sag/swell module and the alert module) from the ION Reference, from the website: http://www.schneider-electric.com/en/download/document/7EN02-0290/

Hopefully some of this information will be helpful to you.

Alana

Reply
sesa389533_brid
sesa389533_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-06-14 08:52 AM

0 Likes
1
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-14 08:52 AM

Hi Alana,

Thanks for your answer, I know that there is a modbus registers map for EN50160 but when I check those registers, they are all at 0. Maybe i have not activated correctly the function En50160 in ION7650 ? This table store the previous observation values ?

Regards,

Francois

Reply
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-06-14 09:13 AM

0 Likes
0
1189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-14 09:13 AM

Hi Francois

You might want to confirm that you have configured your nominal PQ values. If your nominal voltage is set to 0, PQ functions are not enabled.

You can configure your nominal voltage by going into ION Setup, Setup Assistant, Power Quality and selecting the Sag/Swell tab. Select the Nominal Voltage field and click Edit. Ensure this value matches your power system's nominal voltage.

You may also need to enable the EN50160 features. In the latest version of ION Setup, this is available in the Setup Assistant, Power Quality, Advanced PQ tab. Select EN50160 Enable and click Edit. Select On from the drop down list.

To get the latest version of ION Setup, go to the ION Setup Help, and click Check for Update. It is also available here:

https://schneider-electric.app.box.com/ionsetuplatest

There is also a technical note detailing how EN50160 is implemented on your meter. It can be downloaded from the website here:

http://www.schneider-electric.com/en/download/document/7EN72-0197/

Hope this helps,

Alana

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of