Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84599members
353865posts

ION9000 PQ Alarm in Modbus and IEC61850

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa108084_brid
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
1
483

ION9000 PQ Alarm in Modbus and IEC61850

Good day

 

What is the simplest way to read PQ alarm (ie: sag/swell, magnitude, duration, time/date) from ION9000 when using 3rd Party Software?

Since, those are not available in modbus/iec61850 native register

TQ
EY

 


Accepted Solutions
Charles_Murison
Picard Picard
Picard

Re: ION9000 PQ Alarm in Modbus and IEC61850

Hello @sesa108084_brid  (Please consider updating display name from sesa)

 

The answer depends on what information you are wanting to get out of the meter. If you are looking for historical information store in the onboard logs, ION is the protocol to get this information. If you are looking for information about that last sag/swell, then you can customize both IEC61850 or Modbus to give you that data. Note that IEC61850 is limited to just 16 additional analog measurements, modbus has a much larger number of registers available.


https://www.youtube.com/watch?v=C6qiEdUC4x0

https://www.youtube.com/watch?v=qOH7akVJaSo

 

If you are looking for more than just the last PQ event you could possible use store modules to keep some history, depending on what information you want to store and how many events back will determine the number of store modules needed. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
1 Reply 1
Charles_Murison
Picard Picard
Picard

Re: ION9000 PQ Alarm in Modbus and IEC61850

Hello @sesa108084_brid  (Please consider updating display name from sesa)

 

The answer depends on what information you are wanting to get out of the meter. If you are looking for historical information store in the onboard logs, ION is the protocol to get this information. If you are looking for information about that last sag/swell, then you can customize both IEC61850 or Modbus to give you that data. Note that IEC61850 is limited to just 16 additional analog measurements, modbus has a much larger number of registers available.


https://www.youtube.com/watch?v=C6qiEdUC4x0

https://www.youtube.com/watch?v=qOH7akVJaSo

 

If you are looking for more than just the last PQ event you could possible use store modules to keep some history, depending on what information you want to store and how many events back will determine the number of store modules needed. 

 