The voltage input terminals for the Powerlogic and ION meters have a fixed input impedance. The burden can be calculated thus:
VA per phase = (Input Voltage^2) / (Input impedance)
Kindly refer to the installation guide for your meter's for specifications. All meter documentation can be found in the Schneider Electric website: http://www.schneider-electric.com