Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
This module's count register does not have a specific setup register to define the rollover value. Likely this is 2^32-1. If you want to setup a specific rollover value, you could like the Digital In trigger output register to a counter module with a defined rollover value.
Please note that this count can also be reset from external factor (Digital count reset pulse)
Link copied. Please paste this link to share this article on your social media post.
This module's count register does not have a specific setup register to define the rollover value. Likely this is 2^32-1. If you want to setup a specific rollover value, you could like the Digital In trigger output register to a counter module with a defined rollover value.
Please note that this count can also be reset from external factor (Digital count reset pulse)
Link copied. Please paste this link to share this article on your social media post.
Hi Charles,
thank you very m,uch for your fast reply.
To define the rollover value is not necessary in my case. I just want te be sure that the rollover value will not reached in my lifetime 😉
Best regards