Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
This module's count register does not have a specific setup register to define the rollover value. Likely this is 2^32-1. If you want to setup a specific rollover value, you could like the Digital In trigger output register to a counter module with a defined rollover value.
Please note that this count can also be reset from external factor (Digital count reset pulse)
Link copied. Please paste this link to share this article on your social media post.
This module's count register does not have a specific setup register to define the rollover value. Likely this is 2^32-1. If you want to setup a specific rollover value, you could like the Digital In trigger output register to a counter module with a defined rollover value.
Please note that this count can also be reset from external factor (Digital count reset pulse)
Link copied. Please paste this link to share this article on your social media post.
Hi Charles,
thank you very m,uch for your fast reply.
To define the rollover value is not necessary in my case. I just want te be sure that the rollover value will not reached in my lifetime 😉
Best regards
Sven
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.