Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Good day
is there any default modbus register for the following?
1) voltage sag alarm
2) voltage sag magnitude, duration and time/date
TQ
EY
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa108084_brid (please consider updating your name)
The default modbus mapping does not include these parameters however it is possible to add them to the mapping. The user guide should include a section on using IN Setup to add custom mapping. One Item to consider, the sag/swell event could be very short and occurred between modbus polls. You would either need to use a oneshot timer to latch the state or possibly use the sag/swell count and if you see an increment in this value know that a sag/swell has occurred.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa108084_brid (please consider updating your name)
The default modbus mapping does not include these parameters however it is possible to add them to the mapping. The user guide should include a section on using IN Setup to add custom mapping. One Item to consider, the sag/swell event could be very short and occurred between modbus polls. You would either need to use a oneshot timer to latch the state or possibly use the sag/swell count and if you see an increment in this value know that a sag/swell has occurred.
Regards,
Charles
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.