Good day
is there any default modbus register for the following?
1) voltage sag alarm
2) voltage sag magnitude, duration and time/date
TQ
EY
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa108084_brid (please consider updating your name)
The default modbus mapping does not include these parameters however it is possible to add them to the mapping. The user guide should include a section on using IN Setup to add custom mapping. One Item to consider, the sag/swell event could be very short and occurred between modbus polls. You would either need to use a oneshot timer to latch the state or possibly use the sag/swell count and if you see an increment in this value know that a sag/swell has occurred.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa108084_brid (please consider updating your name)
The default modbus mapping does not include these parameters however it is possible to add them to the mapping. The user guide should include a section on using IN Setup to add custom mapping. One Item to consider, the sag/swell event could be very short and occurred between modbus polls. You would either need to use a oneshot timer to latch the state or possibly use the sag/swell count and if you see an increment in this value know that a sag/swell has occurred.
Regards,
Charles