Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello,
When a transient occurs, the history is only displayed on the event screen.
Is there a way to get this information to appear on the Historical Alarms screen?
We have received feedback from customers that it is difficult to manage because an alarm icon is not displayed even when a transient is detected.
This may be possible using designer software. However, not all customers can use this designer software and are looking for an easy solution.
Regards,
Miyai
Link copied. Please paste this link to share this article on your social media post.
Hello @Mehran_Mehrnia and @Miyai ,
I have confirmed that not all modules will be able to write to the meter's Historical alarm log. The transient module was not designed to write to the meter's alarm log seen in the front panel. This is not a setting issue, this is a firmware design decision.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Miyai
As mentioned in ION9000 user guide, Alarm event priorities, Transient alarms which are triggered by voltage transient activity, will be displayed and logged depending on the alarms priorities correspond to event priority ranges:
Alarms with a priority of 'Info Only' or 'None' are not shown on the meter’s display, and do not function as alarms.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hello, @Mehran_Mehrnia
I understand this part of the manual.
I have alarms set as high priority.
I varied the voltage and checked, and the event display showed a history of transients.
However, the alarm icon and alarm history do not show the transients.
I am using the latest firmware and templates.
(V4.6.0)
Regards,
Miyai
Link copied. Please paste this link to share this article on your social media post.
Hello @Miyai ,
When you say you varied the voltage, can you give a few more details? Possibly some photos of the screens would also be helpful.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Charles_Murison
I am currently on a business trip so I will upload the details later.
Regards,
Miyai
Link copied. Please paste this link to share this article on your social media post.
Hello, @Charles_Murison
ION9000 properly detects the transient.
This can be confirmed by looking at the event history.
However, historical alarms do not include any transient information and no alarm icon is displayed.
Transient alarm priority is high.
I assume that with this setting, transient will generally be displayed in the historical alarm and alarm icon.
Regards,
Miyai
Link copied. Please paste this link to share this article on your social media post.
Hi @Miyai
I got the same result even in different fw V4.5, means I can see the Transient related event such as 'Tr1 TranV1Max' only in the Events page but not in Historical Alarm page:
Hi @Charles_Murison
Could you advise if something is missing here, given that in this example, the Transient setup and alarm priority have been set in a way to cover a transient incident with a TranV1Max of 298(which is above the 150%) and related event has been logged:
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hello @Mehran_Mehrnia and @Miyai ,
I have confirmed that not all modules will be able to write to the meter's Historical alarm log. The transient module was not designed to write to the meter's alarm log seen in the front panel. This is not a setting issue, this is a firmware design decision.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello, @Charles_Murison , @Mehran_Mehrnia
Do you know if Schneider has plans to improve this issue?
This issue remains the same between V3.1.0 to V4.6.0.
(I don't know about versions below 3.1.0)
Customers have complained that it is an operational inconvenience.
Regards,
Miyai
Link copied. Please paste this link to share this article on your social media post.
Hi @Miyai
I would suggest reaching out to your Schneider sales team to request the addition of a feature to display historical alarms for transient events. While this does not guarantee implementation, feature requests are the only way to potentially get such additions.
Best Regards,
-Mehran
L3 Expert Advanced metering
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.