Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello ,
Please help me configure the Relay output of ION7650 which requires to have one pulse output for every 15mins Demand (KW).
I am having a challenge on what source to use as a trigger for the relay output, using ION setup for this requirement and there are no power monitoring software for this project.
Please help me resolve this requirement.
Thank you very much!
Jeric
Link copied. Please paste this link to share this article on your social media post.
Dear Jeric,
The Interval End output of the Sliding Window Demand module can be connected to the Pulser module then set the port to any relay you want.
The default framework has provided this function already(as I remember) you just go to the pulser module then assign the port.
Yut