Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7650 COMTRADE Time Stamps

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7650 COMTRADE Time Stamps
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Nicholas_Brown
Nicholas_Brown Explorer
Explorer

Posted: ‎2024-01-26 02:22 PM . Last Modified: ‎2024-01-26 02:24 PM

0 Likes
2
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-26 02:22 PM

ION7650 COMTRADE Time Stamps

Hi, I have a customer that utilizes COMTRADE waveform files for Sag/Swell Waveforms from our ION7650 metering.

 

They are seeing some behavior that they would like to get clarity on regarding the two Date/Time stamps that are reported in the .cfg Configuration file (the First Data Value, and the Trigger Point). 

 

In most cases, the .cfg file will have a First Data Value timestamp that is before the Trigger Point timestamp.  I believe this was their expected behaviour, as we are typically/always capturing pre-event cycles and should be getting some data points before the Trigger.  

 

However, they are also seeing that occasionally, the Trigger Point time is being represented as occuring before the First Data Value.  They are interpreting this as meaning that the Trigger of the waveform is occuring before the data is being captured.

 

They are curious to better understand these two Date/Time stamps and what they mean, and maybe some information on what conditions may dictate them happening in difference sequences.

 

Thanks for any help.

Labels
  • Labels:
  • ION7000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-01-29 08:36 AM

0 Likes
1
1530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-29 08:36 AM

Hello @Nicholas_Brown ,

 

The description of time of first point and time of trigger is true under most conditions. The time of trigger is when the pulse was received by the waveform recorder module. The time of first point is the time stamp of the first sample inside the record.

 

There is a way for meter with pre-event cycles to still have a trigger time before the first sample time. If a meter is currently recording a waveform and a second pulse is received by the waveform recorder, the meter will finish the current record a then start a new record as soon as the first recording finished. When this happens the second waveform has a trigger time before the start of the first point in the second record.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-01-29 08:36 AM

0 Likes
1
1530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-29 08:36 AM

Hello @Nicholas_Brown ,

 

The description of time of first point and time of trigger is true under most conditions. The time of trigger is when the pulse was received by the waveform recorder module. The time of first point is the time stamp of the first sample inside the record.

 

There is a way for meter with pre-event cycles to still have a trigger time before the first sample time. If a meter is currently recording a waveform and a second pulse is received by the waveform recorder, the meter will finish the current record a then start a new record as soon as the first recording finished. When this happens the second waveform has a trigger time before the start of the first point in the second record.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Nicholas_Brown
Nicholas_Brown Explorer
Explorer

Posted: ‎2024-01-29 09:39 AM

0 Likes
0
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-01-29 09:39 AM

That makes complete sense, thank you @Charles_Murison 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore