Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7650 Alert Module to trigger emails on a DI

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7650 Alert Module to trigger emails on a DI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Kevin_Morin
Kevin_Morin Mentor
Mentor

Posted: ‎2017-10-03 11:13 AM

0 Likes
2
1964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-03 11:13 AM

ION7650 Alert Module to trigger emails on a DI

Does anyone have experience in configuring a 7650's alert module to send out email alarm notifications when a pulse is received?

Looking specifically for help in steps needed to map the input to an alarm.

Critical Power EcoXpert Program Director
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa64419
sesa64419 Leader
Leader

Posted: ‎2017-10-03 01:31 PM

2 Likes
0
1915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-03 01:31 PM

Hi Kevin

I have not actually done this particular type of alert myself, but looking at the Digital Input and the Alert modules it seems relatively straightforward.

First off, you need to make sure that your ION7550 has a SMTP server configured.

Access your meter using ION Setup.

Open the Setup Assistant. Go to Communications > Network settings and fill out the SMTP server info.

Access your meter with ION Setup Advanced mode by CTRL-clicking on your meter.

Go to the Alert Modules folder

Right-click and select Insert Module

Double-click the new Alert module to access the registers

On the Inputs tab select Trigger and click Edit. 

Navigate to the Digital In modules, select the digital input you want (such as DI-S1) and select the Trig output (DI-S1Trig)

Configure the setup registers as described in the Alert Module > Details of Operation > Alerting via email

Test by triggering the digital input and making sure you get an email.

Here is a link to the Alert module in the ION Reference

https://www.productinfo.schneider-electric.com/portals/ui/pm8000/viewer/595e26f146e0fb0001f6ffc4/595...

You can also access the whole ION Reference from Available Publications (and get information about the other ION modules) with this link:

https://www.productinfo.schneider-electric.com/portals/ui/pm8000/

Cheers,

Alana

See Answer In Context

Reply
Replies 2
sesa64419
sesa64419 Leader
Leader

Posted: ‎2017-10-03 01:31 PM

2 Likes
0
1915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-03 01:31 PM

Hi Kevin

I have not actually done this particular type of alert myself, but looking at the Digital Input and the Alert modules it seems relatively straightforward.

First off, you need to make sure that your ION7550 has a SMTP server configured.

Access your meter using ION Setup.

Open the Setup Assistant. Go to Communications > Network settings and fill out the SMTP server info.

Access your meter with ION Setup Advanced mode by CTRL-clicking on your meter.

Go to the Alert Modules folder

Right-click and select Insert Module

Double-click the new Alert module to access the registers

On the Inputs tab select Trigger and click Edit. 

Navigate to the Digital In modules, select the digital input you want (such as DI-S1) and select the Trig output (DI-S1Trig)

Configure the setup registers as described in the Alert Module > Details of Operation > Alerting via email

Test by triggering the digital input and making sure you get an email.

Here is a link to the Alert module in the ION Reference

https://www.productinfo.schneider-electric.com/portals/ui/pm8000/viewer/595e26f146e0fb0001f6ffc4/595...

You can also access the whole ION Reference from Available Publications (and get information about the other ION modules) with this link:

https://www.productinfo.schneider-electric.com/portals/ui/pm8000/

Cheers,

Alana

Reply
gord_integris-t
gord_integris-t
Contributor

Posted: ‎2017-10-10 12:08 PM

0 Likes
0
1915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-10-10 12:08 PM

The easiest way I've found is to use a setpoint module which creates an "on" trigger which you can use to trigger the alert. To test I use a pulse merge module and merge an external trigger and and the setpoint module into the alert trigger. Hope that helps.

If not, give me a bit more info and I'll see what I can do.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore