Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7330 & ION7350 TCP

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7330 & ION7350 TCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
EvonneYin
EvonneYin Explorer
Explorer

Posted: β€Ž2014-06-19 11:13 PM

0 Likes
5
2242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2014-06-19 11:13 PM

ION7330 & ION7350 TCP

Hi All,

How many concurrent TCP connections an ION7330 and ION7350 can support?

Same question as the PM5000 series

but for ION7330 and ION7350?

Many thanks!

Evonne

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JamesAZZO
JamesAZZO
Leader

Posted: β€Ž2014-06-20 02:15 AM

0 Likes
4
2166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2014-06-20 02:15 AM

1x for each protocol/port. πŸ™‚ Unfortunately, as many have found out the hard way. You cannot have multiple people reading ION on 7700 or Modbus TCP 502, or EtherGates (7801 and 7802)

Can someone please post KB 200829 - Ethernet ports and socket summary on ION meters? (it must have been updated since 2009, which is the copy I have)

Also see RESL183645, & RESL199661, & RESL194118

See Answer In Context

Reply
Replies 5
JamesAZZO
JamesAZZO
Leader

Posted: β€Ž2014-06-20 02:15 AM

0 Likes
4
2166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2014-06-20 02:15 AM

1x for each protocol/port. πŸ™‚ Unfortunately, as many have found out the hard way. You cannot have multiple people reading ION on 7700 or Modbus TCP 502, or EtherGates (7801 and 7802)

Can someone please post KB 200829 - Ethernet ports and socket summary on ION meters? (it must have been updated since 2009, which is the copy I have)

Also see RESL183645, & RESL199661, & RESL194118

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: β€Ž2014-06-20 08:52 AM

1 Like
2
2166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2014-06-20 08:52 AM

There should be an option to disable one or both the serial ports and "convert" them to a TCP socket connection.  Check the list of protocols on the serial port and see if there is a "disable" option.  That should allow an additional connection to be made.

Note that the additional connections are still multiplexed over the internal serial port between the ethernet card and the main meter so there may be a slight performance drop.

If how to do this post back here and I will have a quick look.  When I wrote this code years ago I seem to remember adding this feature in but it may not be the most obvious how to turn it on.

Reply
JamesAZZO
JamesAZZO
Leader

Posted: β€Ž2014-06-20 07:11 PM

0 Likes
1
2166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2014-06-20 07:11 PM

Hi Hal! Sounds like an interesting workaround. However, I have never seen "disabled" as a setting that you could choose on any of the serial ports. This is just from my memory, but I think your only options are ION, Modbus RTU, DNP 3.0, and in the case of COM EtherGate as well.

Reply
EvonneYin
EvonneYin Explorer
Explorer

Posted: β€Ž2014-06-22 04:54 PM

0 Likes
0
2166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2014-06-22 04:54 PM

Thank you. I knew I can count on you guys.

πŸ˜ƒ

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: β€Ž2014-06-23 10:12 AM

0 Likes
0
2166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2014-06-23 10:12 AM

Hmm.  You are right.  I just checked on some of the devices in the our lab and they don't have that option.  I seem to remember we did this during development though.  Maybe it is an option only in the latest ethernet card firmware. I am not sure how we ended up doing it - it was a *long* time ago that code was written.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore