ION IEEE 519 program questions

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION IEEE 519 program questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
conradvr_hexeis
Lieutenant JG conradvr_hexeis
Lieutenant JG

Posted: ‎2022-12-12 11:33 PM

1 Like
5
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-12 11:33 PM

ION IEEE 519 program questions

I have been looking at the IEEE 510 ION code for the ION7650 and have a few questions about some of the formulas used.  I haven't looked at the ION7400 or ION9000 code yet.

 

Q1.  The framework requires the manual entry of Fault Current Isc and Demand Current IL.  The ION code calculates the Isc/IL ratio using these entries.  The code also calculates Isc/IL Actual using 3 parts of code.

Part 1: There are three Demand modules to calculate the Demand Phase Current. 

Part 2: These are connected to three Maximum modules to calculate the three Peak Demand Phase Currents 

Part 3: The code then calculates Isc/IL Actual = Isc / SUM of the 3 Peak Demand Currents.   

Question: Why are the Phase Current summed? Shouldn't the formula be Isc/IL Actual = Isc / Maximum of the 3 Peak Currents?

 

Q2.  The code sets IEEE519_I_Dmd = Manually entered Demand IL / 3.  It then uses the IEEE519_I_Dmd  as the input Max Demand to the three Current Harmonics Measurement Modules, meaning the Harmonic % values are a % of IL/3 and not a % of IL.

Question: Why are they using IL/3 and not IL as the Max Demand value input?

Labels
  • Labels:
  • ION7000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2022-12-15 09:11 AM

1 Like
1
1755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-15 09:11 AM

On another note to your discussion what is better approximation for ION7650 IEEE519:2014 IL parameter - Average or Maximum of the 3 Peak Demand Currents, what should be the IEEE519:2022 IL as entered value and how to get it?
 

IEEE 519 2002 Il.JPG

 

See Answer In Context

Reply
Replies 5
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2022-12-13 05:38 AM

0 Likes
0
1803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 05:38 AM

As Isc represents 3-phase short-circuit current within a LV installation, my guess is that SUM of the 3 Peak Demand Currents represents the best approximation of maximum demand load current at PCC under normal load operating conditions, even those Peaks may not be coincidental. 

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-12-13 02:35 PM . Last Modified: ‎2022-12-13 02:36 PM

0 Likes
3
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 02:35 PM

When you use the word "code" (in several places in your question), are you ONLY referring to user-customizable framework logic in a custom, non-shipping framework developed for the ION7650 (pre 2014), or are you instead referring to PME, software report, or other software "code"?

For what it's worth: The ION7400 and ION9000 framework logic was completely updated and refactored for IEEE519:2014

 

In either case, I strongly recommend using with configuration wizard as part of ION Setup for configuring ION meters (and especially in regards to IEEE519 configuration)

Reply
conradvr_hexeis
Lieutenant JG conradvr_hexeis
Lieutenant JG

Posted: ‎2022-12-13 04:40 PM

2 Likes
2
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 04:40 PM

Hi @DanL ,

 

Correct, I was looking at the ION Framework using Designer, we call this the code.  Also confirming we use ION Setup to configure these modules.  The reason I am looking at the ION Modules is the V & I harmonics data in the IEEE 519 report didn't look correct.

 

I have powered up an ION9000 on the test bench and had a look at its ION Framework and it is programed as I expected.  The differences are summarized below: 

 

1. The ION7650 Actual Isc/IL is approximately 1/3x actual.

-- The Actual_IDmdMax should be maximum of the 3 Phase Demands not the SUM.

-- This value is no longer calculated in the ION9000

 

2. The Current TDD is about 3x actual

-- The Max Demand input to the three Harmonics Measurement Modules should be the entered IL and not IL/3

- The ION9000 uses the IL as entered

 

3. The Current Individual harmonics as a % of max Demand are 3x actual

-- The Max Demand input to the three Harmonics Measurement Modules should be the entered IL and not IL/3 

- The ION9000 uses the IL as entered

 

Can you please confirm these findings, as if they are correct the TDD, I Harmonic% and Actual Isc/IL data generated by the ION7650 is significantly incorrect.  To rectify this issue, the formulas in the Arithmetic Module (screenshot below) can be updated, leaving all the other modules as is.

 

conradvr_hexeis_1-1670977910685.png

 

conradvr_hexeis_0-1670977815287.png

 

 

Reply
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2022-12-15 09:11 AM

1 Like
1
1756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-15 09:11 AM

On another note to your discussion what is better approximation for ION7650 IEEE519:2014 IL parameter - Average or Maximum of the 3 Peak Demand Currents, what should be the IEEE519:2022 IL as entered value and how to get it?
 

IEEE 519 2002 Il.JPG

 

Reply
conradvr_hexeis
Lieutenant JG conradvr_hexeis
Lieutenant JG

Posted: ‎2022-12-20 11:10 PM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-20 11:10 PM

Hi @Bojan, generally IL will be calculated as the mean/average of the monthly maximum demand over the last 12 months.   Ideally you need to get access to 12 months of Demand Current data.  On sites that don't have this data we generally use the 15/30-minute interval kWh and/or kVA data from private or Utility meters.  If you can't get this data, here we use the monthly power bills as they detail monthly maximum Demand kVA and we convert this into Maximum Demand Current, add up the last 12 months and divide by 12 to use for IL.

 

Given the site's phase loads should be balanced, using the 3 phase average or the maximum of the 3 phases will yield a similar IL value.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of